what type of current supply is given to house holds?
Answers were Sorted based on User's Feedback
Answer / madhuri
AC SUPPLY BECAUSE IT IS ALTERNATING ONE AND IT CAN CHANGE
DIRECTION AND CAN CHANGE BOTH MAGNITUDE AND DIRECTION. SO
SUPPLY OF HIGH VOLT CAN BE REDUCED TO LOW VOLT AND THEN
GIVE TO A DOMESTIC PURPOSE. SUPPLY OF 240V IS GIVEN TO A HOUSES.
IF DC IS GIVEN THEN HIGH VOLT CAN NOT ABLE TO REDUCE TO 240V
HENCE THERE IS A CHANCE OF BURN OUT OF THE METER
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / puneet kulshreshtha
SINGLE PHASE 230 V A.C
OR 3 PHASE 440 V A.C
| Is This Answer Correct ? | 14 Yes | 9 No |
Answer / syam mohan
normally single phase 230v supply but in some cases 415v
three phase supply
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / mukesh yadav
singal phase a.c supply of 50 hz, 230 volt, but in some cases 3 phase 430 volt also given
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sachin kumar chauhan
blow 5KW single phase 230V A.C. 50hz throw single phase
energy meter & abow 5KW three phase with netral 415V A.C.
50hz.throw three phase energy meter.the earth is compalsory.
| Is This Answer Correct ? | 0 Yes | 2 No |
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
WHAT IS B & C CLASS SURGE PROTECTION AND WHAT IS DIFFERENCE BETWEEN B & c CLASS SP
IN PLATE EARTHING , PLATE LAID IN VERTICAL POSITION ,WHY HORIZONTAL WHY NOT
What is the difference between XLPE & FRLS cables? Is FRLS cables is a type of XLPE cable or both r different?
Current Transformer's star point must face the protected object for the relay operation?
what is the design voltage for 6.6KV 2000 KVAR HT capacitor?
What is the formula to calculate the rating of a three phase miniature circuit breaker
How to work definite,over pluxing,revers power,OSR relay
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
What is the de rating factor of cable? What is the importance of the de rating factor in cable select
in case dc we mark as + ve & -ve..but in case a.c. we mark as ph&N...Y LIKE PLZ TELL ME
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)