Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have one DP transmitter of range 0-500mmWC i have to
calculate its range in M3/hr for flow measurement so whats
the formula.

Answers were Sorted based on User's Feedback



I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow meas..

Answer / sam

You first need to have a flow element like a orifice plate
installed in order to get a differential pressure across the
orifice. You then need to measure this differential pressure
with the differential pressure transmitter or a u-tube or
two pressure gauges at various flow rates. If this is not
possible the orifice plate manufacturer will give you the
minimum and max diff pressure across the orifice plate for
various flow rates and liquids. You should already have the
pipe size, the orifice plate details and the liquid you will
use in this application.
Once you have this minimum and maximum diff pressures for
the minimum and max flow rates you can see on the
transmitter range if it will be big enough to measure these
diff pressures. The signal can be send from the transmitter
directly to the DCS and the squire roof extraction can be
done there or you can do the SQ extraction on the
transmitter itself by modifying it's configuration to
measure flow.

Is This Answer Correct ?    12 Yes 2 No

I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow meas..

Answer / kannan.r

range of dp tx and range of output is entirely different.
first of all to measure flow, we need primary elements like
ventury tube, flow nozzle, annubar which will restrict the
flow and so that dp will create.
from the manufacture of the primary element itself the
constant value should be noted. then only we can calculate
the flow using dp tx.

Is This Answer Correct ?    6 Yes 4 No

I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow meas..

Answer / umashankar soni

DP transmitter are used for flow measurement in combination
with flow obstructing devices such as
venturi,orifice,nozzle or aerofoil,which have tested
characteristics i.e. pressure drop across them for a
perticular flow.

This characteristic is then used with DP transmitter to
measure flow.

Is This Answer Correct ?    7 Yes 8 No

I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow meas..

Answer / sarma

simply measure dp at max flow. caliberate dptx to that
value. select output sqrt in dptx. if its out of range of
dptx. adjust orifice and try.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

what is loop1 and loop2 in MTS LT?

0 Answers   SPGC,


Why went

9 Answers  


What are different type of instrument cable

0 Answers   KOC,


What is difference between ESD and PLC please Explain me clearly.

0 Answers  


what is the importance of CV in the control valves? how it is calculated?

0 Answers  


If range of 3-15 psi, a multiplying relay with a 1:2 ratio would give what output pressure for 6 psi input?

1 Answers  


What is loop1 and loop2 in MTS LT?

0 Answers  


Identify the electrical variable that is either directly or inferentially used by various instruments to determine the value of a measured variable.

4 Answers  


can a control valve works without positioner?why need tunning of c/v?

4 Answers  


I have applied the post Junior Engineer-(TM)in R.R.B CHANDIGARH recently . what type of question i have to practice and which book ?. can i get any model question paper?

3 Answers   RRB,


Hello friends i need check lists of different instruments during the Erection and commissioning in thermal power plant.Please help me.My Mail id is naba02222@gmail.com/naba02222@rediffmail.com Thanks Nabakishore Biswal

1 Answers  


How to find the range of DP cell Transmitter for measurement of level in closed vessel.

3 Answers   Rosemount,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)