I have one DP transmitter of range 0-500mmWC i have to
calculate its range in M3/hr for flow measurement so whats
the formula.
Answers were Sorted based on User's Feedback
You first need to have a flow element like a orifice plate
installed in order to get a differential pressure across the
orifice. You then need to measure this differential pressure
with the differential pressure transmitter or a u-tube or
two pressure gauges at various flow rates. If this is not
possible the orifice plate manufacturer will give you the
minimum and max diff pressure across the orifice plate for
various flow rates and liquids. You should already have the
pipe size, the orifice plate details and the liquid you will
use in this application.
Once you have this minimum and maximum diff pressures for
the minimum and max flow rates you can see on the
transmitter range if it will be big enough to measure these
diff pressures. The signal can be send from the transmitter
directly to the DCS and the squire roof extraction can be
done there or you can do the SQ extraction on the
transmitter itself by modifying it's configuration to
measure flow.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / kannan.r
range of dp tx and range of output is entirely different.
first of all to measure flow, we need primary elements like
ventury tube, flow nozzle, annubar which will restrict the
flow and so that dp will create.
from the manufacture of the primary element itself the
constant value should be noted. then only we can calculate
the flow using dp tx.
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / umashankar soni
DP transmitter are used for flow measurement in combination
with flow obstructing devices such as
venturi,orifice,nozzle or aerofoil,which have tested
characteristics i.e. pressure drop across them for a
perticular flow.
This characteristic is then used with DP transmitter to
measure flow.
Is This Answer Correct ? | 7 Yes | 8 No |
Answer / sarma
simply measure dp at max flow. caliberate dptx to that
value. select output sqrt in dptx. if its out of range of
dptx. adjust orifice and try.
Is This Answer Correct ? | 1 Yes | 2 No |
What materials are used in thermo wells?
what is meaning of static pressure
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
What does it mean 3/2 sov
What is 1:1 redundancy ?
what is difference between 3 wire and 4 wire RTD sensor?
12 Answers HTA Instrumentation,
why are use only 4 to 20ma. signal.
what happens when the profibus fails while in operation (operation of a valve)?
what is the conductivity sensor output formula and what is the ph sensor output formula?
In 16' pipeline one pcv is installed which is controlled by PT installed at inlet of PCV.If Flowrate in pipeline increases what will happen to pressure at the inlet of pcv.
how can check the loopchecking for valves?
there are two candidates p and q in an election.During the campaign,40% of the voters promised to vote for P ,and rest for Q.however, on the day of election 15% of the voter went back on their promise to vote for P and instead voted for Q. 25% of the voters went back on their promise to vote for Q and instead voted for P.suppose,P lost by two votes,then what was the total no. of voters.