How ElCB tripping if Neutral touch with ground
Answers were Sorted based on User's Feedback
Answer / umesh
elcb is connected in series with the netral & ground,
whenever the neutral touch to the ground then the circuit
will completed, the ELCB will be trip.
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / anil bhatia
The design of ELCB is such way that all current passes
from phase to neutral to complete the path . Any current
passes from phase or neutral to ground sense the circiut
that there is deflection of current and trips it to stop
supply.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / k.prakashchandra
I think only RCCB requires the neutral wire connection and
earth wire connection is for ELCB.If there is any leakage in
neutral wire ,the ELCB trips if neutral comes in contact
with the earth wire.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / thiyagarajan
How does ELCB WORKS?
If we are using a ELCB:
In fault condition or if the circuit is in open condition, current passes through the neutral.
We are connecting the ELCB from neutral to ground.
The fault or open circuit current in the neutral passes to ground and the equipment get protected from the severe shock.
BY,
THIYAGARAJAN.S
Is This Answer Correct ? | 1 Yes | 0 No |
Why we use modulus with voltage in stability equation that is P=[E][V]SIN@/X WHY VOLTAGE IS IN MODE VALUE WHAT IS THE REASON?
what is suroounding current of dg set?
what is the purpose of commutator in DC motor?
how to diffrentiate between ac & dc motors from a distance
What is mean 2XWY
What is the Operating Powerfactor of UPS??? Why??
why the transformer connected like STAR- STAR, DELTA- DELTA, STAR- DELTA, DELTA-STAR ...? why these connections ,,, explain the advantages these connections?
Current Capacity of 55sqmm & 80sqmm conductor
What is an Isolation Xformer? What is the use of it?
what are the protecyion of transformer & generators
why the generating / transmitting voltage is in the order of multiples of 11(ie 11kv,22kv,33kv......)
Can without battery on line UPS,off line UPS or Invertor works please brief.