if u have to run a 300kw moter then what is ur choice HT or
LT switchgear & explain why?

Answers were Sorted based on User's Feedback



if u have to run a 300kw moter then what is ur choice HT or LT switchgear & explain why?..

Answer / muralidaran - itc

It depends on Application. In HT conductor sizes will be
less & also motor will be more compact since current flow
will be less, but insulation level be more.

HT will be my choice, if speed controll is not required.
LT will be my choice, if speed controll is required (VFD)
Since HT VFDs are quiet high in cost.

Is This Answer Correct ?    6 Yes 1 No

if u have to run a 300kw moter then what is ur choice HT or LT switchgear & explain why?..

Answer / vinoth

For 300 KW motor we can use LT switchgear. Current consumption of a 300KW motor will mot be more than 1000A. So LT switch gear is possible to use

Is This Answer Correct ?    7 Yes 3 No

if u have to run a 300kw moter then what is ur choice HT or LT switchgear & explain why?..

Answer / sadam hussain gaad

Depends upon application.
if all other motors are operated on HT/LT then 300 KW motor
should be opertaed on HT/LT respectively.

If your generation is HT and you want operate on LT then
you have to install VCB, Transformer, ACB and size of cable
will be more as compared to HT but less insulation will be
required.

If you want to operate 300 KW on HT then no need of
transformer,ACB, only XLPE cable will be used.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is active power and rective power and power factor

1 Answers  


what is the ohmic value of transformers

1 Answers  


sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.

0 Answers  


galloping in transmission line is due to

2 Answers   DVC,


Percentage losses in power generation?

0 Answers   Nespak, Trimax,






Need help. 3 phase system. Neutral line arced and melted upon connection of connector with 3 phase power. Why would that happen?

4 Answers  


what is the difference between LT & HT Motors

11 Answers   L&T,


why d.c. supply is given to the primary side of generator?

4 Answers  


physical identification of HT & LT panel

0 Answers   Schneider,


Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA ?

2 Answers  


A 400KVA Transformer has 400Hz frequency.if frequency is changed to 50Hz,then what will be the new KVA rating?

2 Answers   ABC,


how can i select the cable ratings

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)