Answer / satya prakash
At first do correct your spelling mistakes which indicates
that how much you are either inclined towards reading books
or chatting etc!
----------------------------
I am giving a detailed explanations of this. 1 Sq mm means
area of the conductor only. But it has its own insulation
thickness around it. If it is a sheathed/unsheathed cable
then accordingly it has nominal thickness of sheath added
and the overal max permissible dia of cable can be found
out. It has its detailed calculations. I am giving ex for 1
Sqmm Single Core Cable.
Unsheathed Cable: Nominal Conductor Area:-1 Sqmm, Nominal
Thickness of insulation:-THn=0.6mm, Max Overal Dia:- 2.7mm.
Max Current Carrying Cap:- 11A.
Soln:- Conductor Dia: PI*D*D/4 = 1
=>D= 1.128mm;
Overal Cable Dia= D+ 2*THn = (1.128+2*0.6)= 2.328. Now
10-15% of flexibility due to air inside the cable is added
with it which is equal to: 2.328+ 15% of 2.328= 2.6778 ~ 2.7mm.
Sheathed Cable: Nominal Conductor Area:-1 Sqmm, Nominal
Thickness of insulation:-THn=0.6mm, Nominal Thickness of
Sheath THSn=0.9,Max Overal Dia:- 4.8mm. Max Current Carrying
Cap:- 11A.(Same as unsheathed)
Soln:- Conductor Dia: PI*D*D/4 = 1
=>D= 1.128mm;
Overal Cable Dia= D+ 2*THn+ 2*THSn= (1.128+2*0.6+2*0.9)=
4.128. Now 10-15% of flexibility due to air inside the cable
is added with it which is equal to: 4.128+ 15% of 4.128=
4.7422 ~ 4.8mm.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / k.prakashchandra
Please use Mozilla Firefox for asking questions to avoid
spelling mistakes
| Is This Answer Correct ? | 1 Yes | 0 No |
why permanent magnet generator have higher frequency of 400hz
What is a soft start?
hoe we can exlain the effect of caoacitor in fans????????
why Square root 3 used for three phase?
what is overflexing in transformer? setting?
At full load wat is the motor p.f And at no load will is the motor p.f?
line and phase voltage relationship?
1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.
What is Surge arrest? How it work?
Earth leakage relay basic knowledge principle
what is the difference between gas group b and gas group c electrical equipment construction wise?
what is the cable size we can use for 11kv and 33kv ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)