in 3phase 50kva dg what is the full load current for single
phase laod
Answers were Sorted based on User's Feedback
Answer / vikrant
40*1000=1.732*415*I*.8
40000=575.024*I
THERE FORE I=40000/575.024=69.562314 AMPS
THEREFOR FULL LOAD AMPS OF 50KVA DG IS=69.56 AMPS
Is This Answer Correct ? | 7 Yes | 3 No |
actually i think that in 3 phase formula is p = ROOT3 VI COS$ AND in 1 phase formula will P = VI COS$
SO 40 *1000 = 220 * 0.8 ( if we consider voltage 220 volt in single phase) 40000 = 176 i
I 40000/176 = 227 AMP
40*1000 = 415*0.8 I( IF WE CONSIDER V 415 VOLT)
40000 = 332I
I= 40000/332 = 120 AMP
Is This Answer Correct ? | 0 Yes | 0 No |
what are check points to be checked while charging switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
Which one is given high energy in same power consumption AC or DC
why and how current drawn by battery charger depends upon the altitude where it is located?
WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off 10kv 20kv 30kv
What is the technical name of Transformer Oil ?
17 Answers Bhel, Don Bosco, Lanco,
What type of bulb used in small size cross symbol boder and original flame type(Deepam)?
What is the PI test stand for transformer and what is the producer to do this test?
Lt trivector meter with ring type CT.Spec of meter are 3x240 v, -/5A. Ring ct spec. are 60/5A, line voltage- IL .66/3.0KV..what is the multiplying factor
What will happen if we give the 3 phase supply to the rotor of slipring induction motor?
What iz main protection of mediuum voltage motors and what iz the standard IR voltage of 6.6 and 11kv motors.
HOW TO FIND THE PRIMARY AND SECONDARY OF TRANSFORMER(IN OFF CONDITION) USING MULTIMETER? IS IT POSSIBLE FIND BY SEEING RESISTANCE???
In layman terms, what is the difference of Dielectric strength and dielectric constant when speaking of an insulating oil