In Increasing temperature why thermocouple used and RTD is
not used. Both RTD and Thermocouple have in Range of uses.
Answers were Sorted based on User's Feedback
Answer / pukhraj_meghwanshi
Because of Linearity. Increasing Temp. Linearity is
decrease of RTD and thermocouple linearity is increase so
it used mostly.
| Is This Answer Correct ? | 38 Yes | 3 No |
Answer / mallu byali
It is depend on linearity and accuracy.
RTD range std 0 to 400
thermocuple more then rtd range depend on requirements
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mugil
Thermocouple Temp range is up to 1320 degree celcious using t/c butRTD Range is only 600 degree celcious.so T/c is using in High Temperature
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / naresh patil
bcoz linearity of thermocouple is greater than RTD & having
range at 0 degree celcius resistance will be 100 ohm.
| Is This Answer Correct ? | 2 Yes | 6 No |
why we use by pas on a positioner? When can a by pass be not used on a positioner ?
What is frequency factor in massflow meter? When using frequency output?
need to calculate flow rate with the help of dp range and orifice bore dia and size. range is 0 to 400 inwc and orifice size is 12 inch 150 # rf and bore dia is 7.180 inch. need to calculation for flow rate
Give me a simple formula to calculate the bore of orifice plate with datas avilable instead of BS 1040.I want to calculate the approximate bore size only.
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
Make a ladder diagram on LSL valve will close, on PSL valve will open and start the motor
How does your previous experience relate to the job you are applying for ?
what are the standards used for earthing instruments in the field?
Why Flow measurement has to use Square Root
why is an oxygen sensor used in a boiler stack
what does mean by analog output trim and where this one used for?
How a oxygen sensor & analyzer work at boiler or furnace, whats the principle & science is beyond this,How O2 sensor sence & convert signal & move toward analyzer & analyzer show reading in percent?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)