What are the protections to be used for Generator?

Answer Posted / renjith v.r

The following are to be used
1.Voltage restraint O/C relay
2. E/F relay
3. stand by E/F relay using CT in neutral earthing conductor
4. Under voltage ,over voltage relay
5. Differential potential relay
6.negative sequence relay
7.Vector surge relay
8.Reverse power and Reverse reactive power relay
9.rotor E/F relay
9.High vibration, oil temperature, Overspeeed and under speed alarm trip

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

plz tell me,ht and lt panel terminals in substations explain beiefly

2352


why moisture formation found in XLPE Armoured cable outer sheath

1341


what is LSR?

1727


During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP

1417


What information we need to prepare relay coordination chart

1860






A 50Hz,4-pole,3-phase,star-connected synchronous motor has a synchronous reactance of 12ohmsper phase and negligible armature resistances.the excitation is such as to give an open-circuit voltage of 13.2kilovolt.the motor is connected to 115kilovolt, 50hertz supplying. what maximum load can be the motor torque,line current and power factor?

1895


how many joints are allowed in underground HT cable of 1 KM

1380


what is PID control in VFD drives?

1513


If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.

1852


what is the Earth Voltages in Power Plants, Sub-stations, Industries, Residential & Commercial Buildings.

1668


Can a generator runs after getting 1st stator earth fault.

964


armature winding of dc machine produce alternating emf then it convert in to dc by using commutator.But only we consider armature resistance why don't we consider inductive reactane effect?

1645


. What is Electrical Life & Mechanical Life of Circuit Breaker? 2. What is Electrial Life & Mechanical Life of Magnetic Contactor? 3. What is RCD, RCCB & RCBO? 4. What is the Between defferance of RCD, RCCB & RCBO?

2842


Differenciate between circuit wiring and sub main wiring with illustrations

1773


Approach of a cooling tower is the difference between temperatures of what factors?

625