Why restricted earth fault protection is needed? Why can’t
differential
Protection is sufficient?
Answers were Sorted based on User's Feedback
Answer / anaz.a
restricted earth fault protection is a protection scheme given in assistance to the differential protection.it is given to protect an earth fault which occurs very close to the neutral point in star connected windings of the transformer.this kind of fault a very low fault current only and this current may not be sufficient to activate the differential protection relays.
The sensitivity of the differential relays cannot be increased beyond a limit since this may lead to unnecessary tripping(the transformer may trip even for an earth fault occurring on the outgoing feeder Side)
Hence a special scheme of protection called REF(Restricted earth fault)is provided in order to protect a restricted area of the winding from internal earth fault.
| Is This Answer Correct ? | 32 Yes | 1 No |
Answer / bandarawy
Due to the fact that current transformers always have a
certain error, the differential current always differs from
zero as soon as there is a load current flowing. Especially
during a through-fault condition with high short circuit
current , the differential current may be very high due to
the error of the current transformers. Depending on the
sensitivity of the setting value of the overcurrent
protection relay, when it is used as a simple differential
protection relay, unwanted tripping may occur.
For this reason, it is necessary to stabilize the
differential protection by means of a so called bias
current. For the restricted earth-fault protection using
the biased differential protection principle
| Is This Answer Correct ? | 3 Yes | 8 No |
How the FM200 Gas Supression System wil Work????
what are the differant std sizes of cable trenches?
What is excitation?
HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?
why designer use kva rating instead of kw in transformer rating???????????????
what is meant by switch fuse unit ?
3 Answers Thermal Powertech Corporation India Ltd TPCIL,
What is knee point voltage of transformer?
Dear all, i completed M.E(Power Electronics & Drives) 2011 passed out having 78% so i need job in core side but i don't know how can i receive the calls from electrical companies and i uploaded my CV in naukri, times jobs etc.. In that iam not recieved any mails from good companies so give me best procedure plzzzzzzzzzzzzzzzzzzzzzzzz..... Thanks, K.Linga Reddy Email-id:-lingareddykmthm@gmail.com Ph no:-08015402078
compressor compresses air means exactly what happens?
I am completed DEEE in tamilnadu, now i am working in andhrapradesh with 2.5 year experience in relavent field. capacity of the tranformer is 11KV, 1MVA Transformer, i am eligible for getting c licence in andhrapradesh pl help me.
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
what is the magnitude of earthing and neutral voltage
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)