Why ACB is used in LT why not in HT and why VCB is used in
HT why not in LT
Answer / iamdon
In ACB(Air Circuit Breaker) arc extinguishing and
insulating is carried out in air medium where as in VCB
(Vaccum Circuit Breaker)it is carried out in low vaccum.
At high voltages, air inonises and losses its dieectric
properties which makes the ACB unsuitable at HT.Thats why
ACB is used at LT not at HT.
Vaccum can suastain high voltage(not ionises) and does not
losses its dielectric properties which makes the VCB
suitable for HT.
Since VCB is costlier and require more maintenance as
compared to ACB.So VCB is not employed for LT where cheaper
option as ACB is available.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 43 Yes | 3 No |
What mean by MLTP
How much area is covered by a single lightning arrestor to protect object from lightning strokes ?
For these 2 devices what their power ratings are ? 1) single phase : AC 220V & starting amps 3Amps (i.e. starting torque) and the stabilized amps 2A ... For deep freezer 2) single phase : AC 220V & starting amps 2.7Amps (i.e. including the starting torque of a CRT monitor) and the stabilized amps 1 Amps thanks
When induction motor is started,we see all other electrial appliances connected on the same supply are dimmed out for some moment why?
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
why humming sound occured in HT transmission lines.
Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three numbers of 1250KVA ,11KV/0.415KV Transformer to feed the Factory load. We have found some abnormality. In one of our Transformers the leakeage current from transformer body to earth through earth continuity wire is almost 86 Amp but in other transformer it is (5-10)Amp. where the load current on three phase and neutral are respectively 1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical person help me about the reasons of this situation and how I can rectify the fault. Moreover,I have measured the earth resistance of the Earth continuity wire which is less than 1 Ohm. Thanks Tapas Barua
what is VFD and where is use of it
What is cable gland,why does use for?
what is the reason for using 110 volt and 60 hertz ac supply for using power distribution in America?
Fot testing new star-delta 132 kw motor in electrical worshop.we should check in star or delta connection as we do not have higher capacity cable in worshop?
why we use two slope(differential & restraining) in differential relay.but in busbar protection differential we are using only one slope?please explain
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)