HI, I want to buy a new Xformer to my plant. what are the
main parameter should I check ( Xformer rating is 16 MVA)
Answers were Sorted based on User's Feedback
Answer / amit goyal
you should check all type of test like Winding
ratio ,Winding resistance,megger value,megnetic balance,
Heat run test,High pressure test, low Pressure test.Air
pressure test,IOVT test,Vector group test, oil BDV test,
| Is This Answer Correct ? | 1 Yes | 0 No |
The MVA Rating here shows that you require a transformer which converts 11 kv to 66 kv. If you want to buy such a heavy transformer , then the seller will itself provide all the details
| Is This Answer Correct ? | 0 Yes | 0 No |
What is meant by power factor correction?
why is the earthing pin on 3 pin top are big and thick
what is buffer resistance starter.?.What is the working principle and where it is used..?
Safety measures in air circuit breaker
5 Answers Megatron Solutions, TCS,
what is earthing.how we make it,describe briefly.
What is the range of the stator resistance of 3 phase induction motor?
A circuit breaker is a
1 unit or 1 kwh means how much kva
What are the three major categories of error?
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
why do we need the body earth?
What is the diffrence in between Class PS & Class 5P10 for CTs
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)