Why consumers are charged based on Kwh basis why not on
Kvah basis.
Answers were Sorted based on User's Feedback
Answer / mahavir jagdev
They can be charged in Kvah only in case of DC transmision. In AC transmission due to the inductive or capacitive load the power factor comes into play, hence the effective metering is done on Kwh basis. Infact the energy company instruct the consumer whow has a lot of inductive load (motors) to put capacitor banks to keep the power factor within 0.85 region for lower powerline losses.
| Is This Answer Correct ? | 10 Yes | 7 No |
Answer / raj
Yeah... now industrial consumers are billed on KVAH only in Andhra Pradesh. Actually, this way of billing is the correct method to curtail low power factor problem in industries. In this case, we calculate the energy as below.
apparent energy,kvah = active power (kw)in each time block /power factor in each time block
Note : 1.presently the meters are designed for 15 minutes blocks.
2. In this billing method, the discoms dont penalize seperately for low power factor(as we already considered in thecalculation of apparent power.)
In the case of domestic, energy is billed for kwh only as it is uneconomical to place trivector meters ( as they consume less power and thier impact is very low on grid compared to industrial consumers )
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / paneeselvam
please anybody help the correct answer for the above question
| Is This Answer Correct ? | 0 Yes | 0 No |
What is Chatoliq Protection ?
How induction stove works?
Ammeter of 1 ohm resistance measure max 10 ohm to measure higher resistance from it
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
Consider three heater bank connected in 3 phase star with neutral.Each heater bank connected in each phase.So each phase get 230 volts supply.my question is,during balance condition, current flow in neutral or Not
what is difference between low voltage and high voltage
21. What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing? 22. What are the protections to be used for Generator? 23. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0 24. What happens when the polarity changes in CT? Explain briefly? 25. Explain the Term in CT Name Plate – Class: 5P10
How to calculate unit consumption on the basis of load. kWH=kwXhrs.is it correct? kw is motor load.What is unit consumption at 100% load, 50% load & on no load.
what type of protection used below 132KV feeders
11 Answers APTransco, Telecommunications, wbsedcl,
Natural frequency of a system gives... 1) nature of transient 2) overshoot 3) oscillations 4) speed of response
define displacement & magnitude ?
If the feeder rating is 7.5 kw or 10 HP star-delta feeder, MCCB is taken as 63 a, contactors-32 a, how much will be the OLR rating or which range OLR should be considered when we concern about type-2 coordination?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)