Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why Batteries & Battery chargers are used in substation?
what is the different between UPS & battery charger?

Answers were Sorted based on User's Feedback



why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / jai prakash

generally we gave dc supply to the all protective equipment
like relays ,indicators , and for all controlling devices
through batteries in substation .

Battery Chargers are basically Automatically Stabilised D.
C. Power Sources meant to feed the connected load and
simultaneously trickle (float) charge the connected Battery,
thereby maintaining it (Battery) continuously healthy &
ready to feed the load in an emergency situation of A.C.
Supply failure. This arragement ensures an uninterrrupted
D.C. Supply to the connected load at all times - by the
Battery Charger in case of A.C. Power Supply availability or
by the Battery in case of failure of A.C. Power Supply.

Is This Answer Correct ?    52 Yes 10 No

why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / muhammad mustaghas

1) The operation of monitoring devices such as relays and
the tripping mechanisms of breakers require an independent
power source, which does not vary with main source being
monitored.Batteries provide this power source for the
successful operation of switching and control devices in
power protection system.
It is therefore necessary to ensure that batteries and
charges are regularly inspected and maintained at the
highest possible level of efficiency at all times to enable
correct opeartion of relays at the correct time.
2)UPS means uninteruptable power supply which accept AC as
input and convert this AC into DC for the storage purpose
and when require AC supply then again it convert DC into AC
for its out put terminal.Basically UPS is used to stored
the energy in from of current to fullfill the requirement
for emergency supply but batteries only provide the DC
power supply to its load and can store and supply the
limited amount of power.

Is This Answer Correct ?    21 Yes 4 No

why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / amit khamesra

In lieu of a more reliable power supply source, DC supply
is used in place of normal AC supply. If there is a
blackout, AC power will not be available n the electrical
protection devices will not operate. To avoid any such
situation, DC supply is used. DC supply is provided by
batteries and charger is used to keep the batteries healthy
by trickle charging the batteries in Float / Boost mode as
required. UPS is an uninteruptable power supply which uses
converter inverter set. AC input is first converted to DC
and again converted to AC. The battery bank installed for
UPS is connected in between converter inverter set so that
if AC supply to converter fails, battery comes on load and
supplies DC to inverter for maintaining the AC power supply
at output end.

Is This Answer Correct ?    17 Yes 9 No

why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / tarun aggarwal ymca

In AC substations if AC power fails, for tripping of Switchgear an alternative supply is needed. This supply is DC supply from Batteries. AC supply can not be stored where as DC can be stored in batteries. Hence all circuit breakers are with DC voltage coils. In case of a line to line fault or line to earth fault the incoming / remote breaker needs to be tripped. At this point AC is not available and hence DC is used. 
While AC over voltage or Under voltage are abnormal conditions and hence AC supply is present hence AC coil can be used. 
For charging of battery, battery charger is used. Charger takes AC voltage, steps down and rectifies in to DC voltage and supplies charging current to battery. 




UPS (Uninterrupted Power Supply), consists of a rectifier, battery and inverter and its output is AC supply. During utility power supply fails, this UPS supplies AC voltage to instruments for monitoring important parameters. But this also depends on Battery. Hence efficiency of UPS is low, as well as reliability is low due to more components. Hence using battery is better for tripping functions in protection circuits. In case AC power fails for longer duration standby DG set is started for charging battery.

Is This Answer Correct ?    10 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between ground and neutral?

2 Answers  


wat is mean by HRC fuse... WHY we choose it...?

3 Answers  


wwht is wave trap used in ht line

4 Answers  


Can the output voltage of a rectifier be greater than the input AC voltage without the use of any voltage multiplier in the circuit??please provide the explanation too..

0 Answers   IOCL,


In scott connected transformer number of turns in the primary winding of teaser transformer is % of number of primary turns of main transformer A 86.6 B 57.7 C 14.4 D 33.3

1 Answers  


I am an electrical power engineer and arranged power system for a data center, I installed MCB, ELCB and erthing system TN-C-S. But some times several ELCBs Disconnect circuits at the same time! what may be the reason? (the ELCBs are 25A ,30mA)

9 Answers  


different aspects of voltage stability

0 Answers  


What is the difference between the transmission line and distribution line?

0 Answers  


What are eddy current and define rms value?

4 Answers   NTPC,


what is the max. acceptable leakage current in 33kv bus bar

0 Answers   Tanesco,


I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase), before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???

1 Answers  


Difference between on line capacitor and Station type capacitor

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)