What is difference between metal clad & metal enclosed
switchgear?
Answers were Sorted based on User's Feedback
Answer / karunakar
Metal-Clad Switchgear is an assembly of units characterized
by the following features:
The main interrupting device is removable and arranged with
a mechanism for moving it
physically between connected and disconnected positions. It
is equipped with self-aligning and
self-coupling primary and secondary disconnecting devices.
The interrupting devices, buses, voltage transformers, and
control power transformers, are
completely enclosed by grounded metal barriers, which have
no intentional openings between
compartments. A metal barrier in front of the interrupting
device ensures that when, in the
connecting position, no live parts are exposed by the
opening of an enclosure door.
All live parts are enclosed within grounded metal
compartments.
The Metal eclosed switchgear assembly consists of multiple
metal-enclosed, vertical sections. Normally the end
sections are designed to allow for installation of future
sections. Each vertical section consists of up to four
individually enclosed breaker or auxiliary compartments.
Compartments are sized to provide uniform height of each
switchgear assembly.
Various components such as circuit breakers,
instrumentation and control equipment, transformers,
relays, three-phase bus work, all internal wiring,
connectors, and other supporting equipment are included in
each assembly. These units can be directly coupled to 480V
motor control centers if desired
| Is This Answer Correct ? | 21 Yes | 5 No |
Answer / gurumurthy.k
The Simple reply is " A metal clad can be a metal enclosed
but a metal enclosed can not be metal clad". Which
means , the Metal enclosed need not have a compartments
within its structure, can have fixed interupting medium and
and safety related issues. These are applicable for a low
coltage swicth board but metal clad is more apt for medium
coltage.
| Is This Answer Correct ? | 15 Yes | 2 No |
how to calculate power consumption in slip ring motor at different step
TYPE'S OF BREKAR ,WHAT IS TRANSFORMAR & SAFTY. STARTER DOL & STAR DELTA STARTER.
does over charging of a battery reduce its life?
is power factor correction related with vector group of transformer i.e:Dyn11?
what is need of air gap in expansion section in busbar?
there are 3 transformers each of 1500 kva and one transformer of 1000kva for a 11 floor building . total otgoing kw is 4066 kw. i need an extra 260 kw .is there any provision for that? what is the max kw that can be connected with these transformers?
why we are using DC supply for all protection relays, why cant we use AC supply..???
what is the purpose of using semiconductors in HT cables
CAN WE GENERATE AC WITHOUT DC EXCITATION?
If the Power Factor of generator is 0.85...What does this mean and Can the motors connected to this generator operate at PF more than 0.85 ?
IN CABLE TRENCH WHY FILL UP THE SAND. AND WHAT IS THE DIFFERENCE BETWEEN OVER HEAD AND UNDER GROUND LAYING THE CABLES
what is hystersis loss?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)