What are the protections used in a HT breaker to protect
the HT motors.
Answers were Sorted based on User's Feedback
Answer / shantanu dash
To protect the HT Motor, Motor protection Relay with the
following protection features are used in HT Breaker. they
are :-
1.Short Circuit
2.Excessive Start time
3.Thermal Overload
4.Locked Rotor during running/start up
5.Unbalance/loss of Phase/single phasing
6.Earth fault
7.Loss of Load
8.Temperature supervision of motor
9.Limitation of No. of Starts/Time between starts
Is This Answer Correct ? | 33 Yes | 3 No |
Answer / sivaraman
We have to use for Motor Protection Relay (SPAM 150C)
1.Short Circuit
2.Excessive Start time
3.Thermal Overload
4.Locked Rotor during running/start up
5.Unbalance/loss of Phase/single phasing
6.Earth fault
7.Loss of Load
8.Temperature supervision of motor
9.Limitation of No. of Starts/Time between starts
All above facilities are available in this relay.
Is This Answer Correct ? | 27 Yes | 2 No |
if power factor comes in leading & showing -0.95. Is there any effect on electrical system? if yes, then please tell me what would be the effects. & how long we keep power factor in leading. Keeping power factor in leading shows more KW & less KVA is it correct or not.
For overhead protection we use which transformer?
how to calculate the starting current of a motor? gopal
how can we measure rotor current of a 3phase wound rotor induction motor connected to liquid resistance starter
why we are using R,Y,B colours for 3 Phase ?
if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will happen?
What is Diff btw Fire Alarm & VESDA System???
what is EIB lighting control system? what is the advantages of this system?
What is stepper motor?
What are the types of excitation system?
How RTCC works with OLTC
What is the need for checking knee point voltage for CT's?