How to calculate the cable size (XLPE)for suitable to 120KW
load (if Motor or heaters etc)
Answers were Sorted based on User's Feedback
Answer / prakashchandra rana
for 120kw motor flc is 180amp at .8 pf so if we run this motor
on star delta starter we will use two numbers of 150sq.mm
cable from starter to motor and its main power cable will be
of 300sq.mm.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / subhash t p
this load should conected with 3 phase
120*1000/440=273amps
we can use 300mm2xlpe cable.
Is This Answer Correct ? | 9 Yes | 8 No |
Answer / malleswr
for 120kw motor flc is 220A so cable size taken 1.5 times
to flc ie 330 300mm2 cable use
Is This Answer Correct ? | 5 Yes | 6 No |