Why we use neutral cable just half from phase cable.Tell me
briefly,please.
Answers were Sorted based on User's Feedback
Answer / umesh kumar
If urLoad is balanced in three Phase supply system Neural
current is Zero . neutral current is always depend on the
Unbalance load. So in Case of 3 phase system neutral wire
taken half of Main wire.
but in case of 1 phase supply system neutral is the return
cunductor and phase current will be equal to neutral curent.
so In 1 phase neural would be of same size.
| Is This Answer Correct ? | 42 Yes | 7 No |
Answer / imran
In three phase neautral has no current. Only at unbalanced
load there is flow of current in nutral that is why it is
half the phase size
| Is This Answer Correct ? | 26 Yes | 7 No |
Answer / ikab
In three phase, current in neutral in one third
of phases so conductor size is less. but in single phase neutral conductor size should be same as phase conductor size.
| Is This Answer Correct ? | 20 Yes | 10 No |
I am in last year of Engineering.I want to apply for ONGC on GATE based score.They require Certificate of Competency as Electrical Supervisor.How can i get this certificate so I can apply for AEE(ELECTRICAL) in 2016
What is the meaning of Fault level rating?
1 Answers Balrampur Chini Mill,
capacitor is load free component but why ampare meter shows current when capacitor bank breaker close?
wat is the role of reactive power in power generation?why we have maintain it.
why we step up voltage for reducing the loss, even if voltage and current are proportional anr resistance remains same
We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.66 how can we maintane it? how can we balance our load?
why transformer rating is in kva?
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase, before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
In Delta connected capcitor bank, One bank failed due to some problem. Can we connect Open delta capacitor bank to 3 phase motor. The motor voltage rating is 6.6KV. IF yes what changes will happen?
suri transmission
WHY FLEXI LINKS ARE USED INBETWEEN GENERATOR TERMINAL OUTPUT & BUS DUCT CONDUCTOR.
How Load Factor, Demand Factor, Diversity Factor etc best applied in designing an electrical circuit? Is it allowed to consider these factors in each and every panel in an electrical distribution system? Can any body suggest a good book for reference?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)