How magnetic balance test of single phase transformer is
done,Especially in ESP transformer rectifier set.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Magnetic balance test is a comparative test.You have to
compare the test results with another identical tr
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / rajrupa chattopadhyay
Magnetic balance test is performed to detect the inter turn
fault in transformer winding. It mainly focus on induced
balance voltege & magnetising current drawn during the test.
Is This Answer Correct ? | 0 Yes | 0 No |
When and where resistance earthing is used ? How to calculate the time constant for earth fault
what is meant by GOD in transmission system ?
our factory is going under construction mean time transformer 1000 kva 2 nos &load break swithch 12 kv & 4 nos 750 kva 2 nos & 380 kva 2 nos generator to be errcted.how to arrange earth pits &how to earth connect & neutral pit how to calculate in earth bit size.
how to increase senstivity of ct
as per BIS supply voltage in India is ......
How can I calculate per unit (KWH) fuel (Gas/ Diesel both) consumption 1MW unit?
Are we do it in single transformer with dual primary as 11 KV and 33 KV and constant output as 415 Volts?.
Is electro plating what type of load whether resistive, inductive or capacitive loads
Why the outpet og DG is 415V not 440V?
During the testing of Electrical Equipment the test cables should not touch the equipments. For that testing engineers use to cotton rope to hang the cable from measuring Equipment to testing equipment terminal. Please explain the technical reason for this practice.
WHAT IS LINE TRAP,HOW IS IT FUNCTION?
what is Over current, earth fault (O/C+E/F) ?