Answer / siddu
NGR Means Neutral Grounding Resistor, used for higher
rating of transformer because to allow the heavy fault
current through it, during the fault so -----NGR resistane
value so less Ex. 9.5 Ohms
low resistance allow the fault current easily
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / raviteja nowduru
NGR stands for neutral grounding resistor.it connected
between neutral point and ground.it is a type of grounding
to limit the current not to eliminate fault currents.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / meka sekhar
NGR means neutral grounding resistors normally connected in
neutral circuit of transformer & generator to limit the
earth fault current. After installing NGR in neutral
circuit, earth fault current will be in the range of few
amps i.e. 5A t0 300 A.
Is This Answer Correct ? | 2 Yes | 0 No |
WHY NOT CONSIDER PROTONS IN ELECTRICITY LIKE ELECTRIC CURRENT?
What is d diff. btw MCB & MCCB???
can someone explain that how the speed of the protection system affects the fault level calculation?
for 1000kva transformer how kvar rating is need for this PFI plant. and how does it will calculate? and Apmpere rating of main cable connection?
6 Answers Engineers India, GCC, KP, QPSL, Siemens,
Please brief working principle & construction of permanent magnet AC Servo motor
what is the rating of a power transformer?
Alternator rotor earth fault relay circuit
what is the use of megger? and types
11 Answers TNEB Tamil Nadu Electricity Board,
resistance switching is used in case of- ? a. air blast CB b. bulk oil CB c. minimum oil CB d. all types of CB
What is GIS Substation and how it operate? where these type of substation installed?
can anybody send the rrb chennai &rrb bopal question papers of 2006&2007.My exam is on 12 oct 2008.Its urgent
what is the problem of generator over voltage.?except automatic voltage regulator card