How to check the SCAN time of DCS ,n dont give therotical
answers .How to check the SCAN time of DCS during FAT?
Answers were Sorted based on User's Feedback
Answer / rajkumar
If you are using a DCS (Distributed Control System), there
should be a diagnostic utility that you can run (this is
usually part of the system software). If your sotware scan
is structured correctly i.e. all software is called in
cyclic scans and not free scans, the utility should be able
to tell you the loading of these scan cycles.
You should also be aware that you are doing this under FAT
conditions. This would imply that most of your IO are not
connected, which in turn would push up your scan times for
all the diagnostic alarms comming in.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rnm
In my opnoin, Sacn time checking during FAT shall be input
simulation with one repeater block. Then go for cycle sacn
rate check, which will cover input,process block(PID) and
output. We know, there wiil be no O/P connected in field
and no much execution of loops. In this case, very
difficult to conclude this time.Better to check I/O
scanning rate.
| Is This Answer Correct ? | 0 Yes | 0 No |
When can a bypass not used on a positioner?
Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?
can you tell me how many stages in steam turbine of 10 MW power plant
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
Describe all types and levels (4-20mA, 0-10V, mV, pulse, etc.)of analog and digital I/O used in process control application.
EXPLAIN NETWORK COMMUNICATION ON DCS?
difference between span and range
what is difference between OP AMP and differential amplifier?
how in the 2 - wire transmitter, 24v supply and the 4ma signal gets in the same path?
Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?
Waht is surge in compressors and how to control it?
Specify eight technical requirements that you would consider important, when deciding upon a particular control valve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)