Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

We have a bank capacitor rating of 60 KVAR for a overall
load of 160 KVA and we have connected three loads of 50KVA
each. We would like to auto matically correct PF using APFC.
How do we design it?

Answer Posted / rachuri_sree

APFC panel should be connected to main incoming busbar i.e.
from where 160 kva load was fed. 60 kvar capacitors should
be devided into smaller capacities i.e you have to use
either 6x10 kvar or 4x 15kvar or 10x6kvar. I will consider
6x10 kvar. in APFC you have to programe each stage
capacity. here the value is 10 kavar. You have to take 6
no. of capcitor switching duty contactros and to be wired
as per the APFC. It also requires one CT signal and voltage
signal(any one of the three phases of main busbar). You can
program s/on and s/off time in APFC. and also you can
program target power factor. EPCOS apfc is the best
controller I have used.

Is This Answer Correct ?    8 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.

1965


how to calculate the earth mat design in 132 kv substation yard ????

6235


i have completed deee and i've (June2012-feb 2015 experience in electrical maintenance in pvt ltd company.company having HT & LT electrical power.how to apply electrical C-license ,NOW I was resigned my job,what are requirements of applying for c-license

1722


What is voltage ratio of a transformer?

1178


how synchronous condenser is used in place of synchronous generator with out negotiating IEEE standards? Can i use 3 generators as synchronous generators and 2 generators as a synchronous condensers in an IEEE 14 bus system with out disturbing the standards?

2119


in 132kv substation CRT means

2618


how to find Harmonics and types as per the equipemnts

1271


what is the maintaining Cf in UPS.

2347


What is conventional thermal current (Ith)

4433


How do I calculate a WTI CT ofa 1250kVA 6600/400V transformer

1742


What happens when two positively charged material is placed together?

1132


what is quality factor in series resonance circuit and calculate the factor of voltage magnification? how it happens?

1956


Please brief working principle & construction of permanent magnet AC Servo motor

2225


in single phase converter, the no.of scr's conducting during overlap a)1 b)2 c)3 d)4

2061


What is the meaning of Insulation H for transformers????

2125