Answer / sareer ahmad lone
Star connection is that connection from where we can take
the neutral point.If you take three coils in a transformer
similar ends are joined together to form a common point
which is called a neutral.We can earth the neutral point.
Normally for bigger transformers like 66kV or more the
connection is star/delta,and the cost is less because the
higher the voltage the more the insulation you have to
use,so if you use a star primary you can degrade the
insulation towards the neutral point,then using less
insulation.Hope the answer is correct
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / satya
star winding is nothing but the connection of three windings
at one point with similar ends
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / sankara babu
star connection is defined as all the conductors connected to a common point is called star connection .
for the higher voltages we are use the star connection due to the insulation problem.
for higher voltages we use the star-star connections.
on secondary side of transformer we always use the star connection with ground confirm
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ashok kumar
in distribution the primary winding is connected in delta
connection and secondry winding is connected star
connection, because to follow the kcl loop.
| Is This Answer Correct ? | 0 Yes | 0 No |
For 35 HP motor how much amount of capacitor should be on in kvr to reduce the current bill
What is single break or Double break related to MCB?
What is the formula to calculate the rating of a three phase air circuit breaker
What is the purpose of Vector Group in transformer?
1 Answers Andritz, ThyssenKrupp,
generator means
freuency meter
what is vibration?
Grounding. Dear all at one of my site we checked the amps at the earthing cable to the alternator it was found 125 to 130 A. at the neutal cable in same machine found 146A. in the same plant checked the earthing current on other alternator it was 52A, and neutral 116 A. we are facing problems with our controller and the card was damaged once. can that neutral/GND current be a reason? as there is common grounding for the Alternator,Brkr panel,Transformer?
Which motor isused in indian railway system?
Why in KVA diesel engine? Why not KW
wat s the electronic device used in the fan regulators recently?
What is Black-out and Brown-out situation in the context of voltage stability in power system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)