Why Current Transformers cannot be connected in parallel
Answers were Sorted based on User's Feedback
i think you know why we are connecting ammeter inseries in
the circuit.now,as we know the current will be flown in a
line thats why ammeter is connected in series.as we know
C.T is used to measure the currents in higher ratings.the
primary of the C.T has less number of turns with thick
conductor therefore the resistance of primary is very low
(R=rho*L/A),if CT is connected in parallel the CT acts as a
short circuit(low resistance of primary of CT).thats y it
will definetly burns out.if any answer is there plz mail me.
Is This Answer Correct ? | 39 Yes | 18 No |
Answer / syamdas
Current transformers are connected in parallel in the
restricted earth fault relay of transformers to nullify the
current, it doesn't burn out the ct's only nullify the
current output.The unbalance current will flow thru the
relay coil and the relay operates.
Is This Answer Correct ? | 22 Yes | 3 No |
Answer / maheswaran
we know that area of cross section of the conductor is
proportional to current flow.. so that we are using thin
conductors.. but the resistance of the conductor is low.
if CT is connected as parallel,it s like a short circuit..
Is This Answer Correct ? | 35 Yes | 21 No |
Answer / martin vester
As can be seen in the different answers this is not a
simple Yes of No question.
It is possible to use CT's directly parallel, but you need
to determine beforehand exactly what kind of CT's you must
use and for what purpose.
Kneepoint voltages must be equal etc.
For protection purposes this principle has been used in
high impedance (earth)differential protection schemes
including possible overvoltage protection (varistor)
In modern differential protection schemes we always use low
impedance inputs and all seperate CT's are connected to
seperate inputs and never set in parallel connection.
The protection will add seperate CT's for one Side if set
properly automatically.
Therefore I would strongly advise caution to just connect
them in parallel without further calculations and demand of
protection and measuring purposes are met.
See manuals on protection schemes for Siemens on:
www.siprotec.com
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / mark fisher
Current transformers should be connected in series to
provide accurate signals for relaying or metering.
A CT has a very low resistance in the secondary winding.
Therefore, connecting two CT's in series does not
significantly alter the resistance of the circuit (i.e.
.0001 ohm + .0001 ohm = .0002 ohm). The voltage drop caused
by the addition of a second CT to the circuit is negligible.
Connecting two independent CT's in series to obtain a "Net
Current" value in a Breaker-and-a-Half configuration is
quite common.
However, connecting two CT's in parallel will result in the
effective resistance of the circuit being significantly
lower than the resistance of either individual CT (i.e.
.0001 ohm // .0001 ohm = .00005 ohm) and will cause the
voltage to be significantly higher (4X) than with a single
CT.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / vineshkumar
Ct connected in series. It has low resistance .so it can measure current properly.if we connect ct is parallel high resistance so current is nulified.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gunasekaran
we can do the parallel connection also but current will be
boosted up. Connection of the ct in series 400/1 ratio same
ct if ur connected in parallel we can get 800/1A ratio.refer
TNEB manual.
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / guest
CURRENT TRANSFORMER NOT CONNECTED IN PARALLEL DUE TO CURRINT
SAME IN SERIES AND DIFFERENT IN PARALLEL ALSO WINDING HAS
BURNED DUE TO SHORT CKT
Is This Answer Correct ? | 10 Yes | 18 No |
who told this???
for relay and energy meters , CT's are connecting in
parellel only.
Is This Answer Correct ? | 9 Yes | 22 No |
What is the acceptable earth resistance for Commissioning the Transformer?
Could u pls tell me the NPCIL electrical engineering interview questions for Executive trainee, and also guide me how to face the interview.
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
why any normal motor have to provide star & delta winding distribution during starting?
what is the safty of poly phase tranformer?
9.The material used for coating the electrode is called........
what is kvarh? Please define it With calculation General motors ?
why tungsten is used in incandescent lamp instead of nichrome though nichrome has high melting point
When oil level in the oltc of power transformer reduces , oil surge relay will act or not
Draw the wave shape of armature current in a generator subjected to a sudden three phase short- circuit at its terminals. Define various reactance of generator from this wave shape.
how many types of colling system it transformers?
If the soil resistivity is more large, how can we earthing our 11 k.v. transmission line?