I have 800 Amps MG Fix type breaker It is in on line & it
has been given only UV (under voltage)coil connection for
tripping purpose.now it is not working properly means its
getting tripp so how can i replace it or how can i rectify
the problem without destrubing my load??????????
Answers were Sorted based on User's Feedback
Answer / sandeep khaire
Short the UV relay contacts used in wiring. Then replace
the UV relay & its contacts.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / karthik
Check with the wiring diagram of the panel and connect the
two wires going to the relay trip coil to a constant
supply.then remove the relay.
Is This Answer Correct ? | 0 Yes | 0 No |
what is meant by trivector meter?
how to reduce the power consumption in office ?
what is power factor? is it good or bad for a system? what will happen if power factor increase or decrease?
State the factors, for the choice of electrical system for an aero turbine.
what kind of material to be used after ngr unit? cu or GI
I have 30 kw motor load & i have selected 10 kvar capacitor bank for power factor improvement.my existing p.f is 0.85 & proposed p.f is 0.99 so ,is it right selection? 2 nd question how to connect c.bank whether in delta or star connection & how to decide it?
how to calculate neutral current in three phase four wire system
how the testing of CT OF 400/200/100 done in33/11 kv s/s
what is electricity
What is the IS standard for MCCB to be use (As per capacity of AMP)& for ACB also.
WHAT IS DIFFRENCE BETWEEN 3 PHASHE AND 1 PHASHE
Please nybody say, weather the result of Bharat Oman is declared or not? Probable date of declare???????