what is the purpose of neutral grounding resistor (NER) and
why?
Answers were Sorted based on User's Feedback
Answer / elizabeth
Neutral Earthing Resistors (NERs) – sometimes called Neutral Grounding Resistors – are employed in medium-voltage AC distribution networks to limit the current that would flow through the neutral point of a transformer or generator in the event of an earth fault. NERs limit fault currents to a value that does not cause any further damage to switchgear, generators or transformers beyond what has already been caused by the fault itself.
| Is This Answer Correct ? | 45 Yes | 2 No |
Answer / maqbool
THE purpose of neutral grounding resistor is to limit the
fault current of the system since ground fault current
takes earth as return path
| Is This Answer Correct ? | 45 Yes | 3 No |
Answer / sajid hussain
Sir I want to install the uat neutral grounding resistor. Where it will connect from and to?. And tell me it's function. Thanks
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / getdaya@yahoo.com
the fault current in power system depend upon the impedence
value of the system,for neutral grounding which provides
high reactance tot the ps ,and low resistance to the ps,
| Is This Answer Correct ? | 2 Yes | 6 No |
Answer / minal
NGR means Neutral grounding resistor. This is connected to
neutral wire to ground the extra leekage current.
Since in UT,UAT & ST star connection is used, that means
there are 4 wires (R,Y,B & N).Thus neutral is grounded with
a resistor.
| Is This Answer Correct ? | 7 Yes | 15 No |
Answer / ramesh
Neutral grounding resistor generally used in star connected
load in order to reduce the over voltages due to either
switching phenomena or lightning phenomena.
Neutral grounding reactor is another component used for the
same purpose.
| Is This Answer Correct ? | 7 Yes | 18 No |
Answer / subhani
any short circuits occur in stator or rotor then that short
circuit current will limitig and any erath fault occur in
rotor or stator then thats current will also limited value
by depending on resisance value
| Is This Answer Correct ? | 1 Yes | 16 No |
how to stop oil leakage in power transformer.
why ht alternators gland plats using brass?
hi pot test principal
3 phase induction motor rotor field rotate at synchronous speed w.r.t ?
What it indicates by 25/41MVA on transformer?
what are the pecularity of shaver sockets ?
In Transformer testing at Shop test we normally test for vector group, open ckt.,short ckt. but what are the other test performed for transformer once it reaches at site.For e.g:if the transformer is dry having rating 1000KVA?
Can you use step up generator transformer of voltage ratio 16.5kv/420kv in place of step up generator transformer 15.75kv / 420 kv
is any body explain me why return current in three phase power system is less then in a red, yellow, blue phases??? as we know Ir+Iy+Ib=In then why nutral wire has less then phase current????
why capacitor using the induction motor?
Why the vector group of excitation transformer in static excitation system is Dy5?
what is the reason for earthing static equipments? why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)