a 3 phase motor was running with delta connected, suddenly
one phase winding got burnt off, what will be the effect ?
Answers were Sorted based on User's Feedback
delta connected winding, one winding burnt off means, its
open circuited. So the motor will work as open delta system
and run normaly with non uniform torque.
The max. load that can carry will be reduced to 57.7% of
full load.
If the motor is connected through a phase faliure relay,
the relay will trip the total ckt.
| Is This Answer Correct ? | 111 Yes | 3 No |
Answer / najib
There are different situations in which this question can
be looked into.
Case 1.The motor is lighly loaded
In such a case the motor shall continue to run at the same
speed without any hiccup.
Case 2.The motor is supplying a rated load
In this case the motor shall draw current more than the
rated valeu and run at a slightly less speed
Case 3.The motor is heavily loaded
In this case the motor shall stop running and chances of
burning of winding is very large
Case 4.The motor is stationary
In this situation the motor shall not start at all.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / kapil bahadure
a 3 phase motor was running with delta connected, suddenly
one phase winding got burnt off,this colled as asingle
phasing.in this condition motor takes large current from
suplly.& large current flow in stater winding. so large
heat produced by stater winding.then burn out motor.
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / b.v. reamon
the effect ---single phasing... motor oveload protection
or MCB will trip and open the circuit.
| Is This Answer Correct ? | 14 Yes | 12 No |
Answer / p.babukumaravel
motor overload protection or MCB will trip and open the circuit
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / anilkumar
3 phase motor running delta connection,if one phase got
burnt means it will work as open delta,it will carry the
load 57.7 percentage of full load and this is called scott
connecton.
| Is This Answer Correct ? | 2 Yes | 5 No |
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
Full form of bdv test?
what are the highly demanded courses for electrical engg. who finished his b.tech
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
EXPLAIN THE APPLICATION OF RECIPROCITY THEOREM
Which circuit breaker arc quenching time is low AC or DC breaker?
Usage of flywheel diode in relays
2. What are the parameters of EHT sub-station?
1 Answers APGenco, Blue Star, Enercon,
1.25 kg of hydrogen are burnt with stiochiometric air, the mass of air in kg required is
why and how fault current flows through ground?
what is relay type VDG,CDG,VTT ect?
i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)