What is the deffrence between Siemens S7-300 & S7-400 PLC?
Answers were Sorted based on User's Feedback
Answer / navdeep
Both are different series of PLC with major difference of
Memory capacity, both have same programming software of
Simatic Step 7, Input Output range vary as per version or
model of PLC used, the memory size of PCMCIA card in both
PLC vary, Data Transmission speed varies in both the PLC,
S7 300 plc are small in size or compact while S7 400
requires separate PSU with the CPU they are bigger in size
compared to s7 300.
| Is This Answer Correct ? | 33 Yes | 1 No |
Answer / taj
Siemens rates the S7-300 as a medium level PLC, and the S7-400 as a high-level PLC. So there are differences in work memory, processor speed, number of communication links and I/O connectivity.
First point, the S7-400 family is rack-based (Multi-pin backplane linking all modules, from power supply to I/Os) whereas the S7-300 is a bus-linked platform (a serial connector links all modules). So essentially the physical layout limits the S7-300 back[plane exchanges to MPI speeds (187,5 Bits per second), whereas the S7-400 uses parallel connections over the backplane rack, permitting higher exchange rates, and a higher module-density.
Second point, the form factor of the S7-300 is smaller, more compact than the S7-400, so this is something to take into account if space is a premium (inside a small machine panel, for example).
Now, the higher S7-300 CPUs (especiatlly for the new S7-317 and S7-319)have specs that approach (and sometimes pass) the specs of lower end S7-400 CPUs, so the distinction is starting to blur.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / guna
S7-300 plc is a mid end plc rated by the Siemens, This
rating is depends on so many constraints but main
consideration on Number of I/O's & Instruction set, No.of
baud-rates, Cost per module. it works on the Simatic
manager driver software. it is available in compact and
modular types. this needs separate flash memory cards
(Removable)in cpu memory to store the data.
S7-400 is a high end plc means its capacity is larger when
compared to s7-300 in all the ways like technically and
physically. it can also work on the simatic manager. S7-400
is also called as DCS (distributed control systems) which
works on the driver software of PCS-7. its memory capacity
is above 64mb(very high).
the hardware configuration of both the plc types differs
a lot.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / guest
s7-300 means we can able to develop a logic upto 300 and
simultaneously 500
| Is This Answer Correct ? | 4 Yes | 20 No |
what is the deference between watt and KVA
at present how many 765 kv lines are there in india?
CPC cable .PVC \1C....I want to get sure that type is flexible indoor or to be install on trench. please advice .thanx :)
IS diode and blocking diode are the same?..what is meant by blocking diode
what is "pu" in electrical engg.
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
Ash AAAC conductor is used for which KV lines
For a 6.6kV Motor it is recommended to do megger test with 500 V d.c and not more than 5kV d.c but the Hi voltage withstand test should be performed by 12kV AC. Why the dc voltage test should be limited but AC voltage withstand test could be with such a high voltage?
what is The difference between national electrical code and I.S.Code (electrical) and what is the value of NEC in electrical engineering field
what is tha online tapping and offline tappchange? which side connected primary or secondary and explain ?
why any inductive load need free wheeling diode?
Dear all, I just want to ask an expert on this forum for some insights. For the magnetic balance test, when applied voltage on a Delta-Star transformer e.g. Dyn11, the following relationships apply for HV side: 1. H1-H2 = H2-H3 H3-H1 2. H2-H3 = H3-H1 H1-H2 3. H3-H1 = H1-H2 H2-H3 For the LV side also: 4. X1-X0 = X2-X0 X3-X0 5. X2-X0 = X3-X0 X1-X0 6. X3-X0 = X1-X0 X2-X0 Is there a similar pattern for Y-d, Y-Y, D-d? And how about Y-z, D-z, Z-y transformers? I've tested a YNzn5 transformer and for LV side I don't see the pattern. In this particular case I got for LV side the following (see values below): H1-H0 H2-H0 H3-H0 X0-X1 X0-X2 X0-X3 128.0 119.9 7.2 29.2 13.3 15.8 70.7 128.4 59.2 23.4 22.0 3.6 7.2 120.1 128.1 13.4 29.3 15.8 What is the relationship here for LV? For row 1 I see the relationship, for row 3 I also see but it's shifted, but for row 2 I don't see such relationship. Any suggestions, answers, someone?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)