HOW CIRCUIT BREAKER RATING CALCULATED?WHAT ARE THE
PARAMETERS CONSIDERED?
Answers were Sorted based on User's Feedback
Answer / asutosh
the breaker rating depends on
1 total incoming supply in kV.
2 total power requirment in kVA.
3 the short circuit power for perticular supply.
Is This Answer Correct ? | 39 Yes | 7 No |
Answer / r p payasi
kVA rating=Sqrt(3)*KV*Fault current(max)
so required is
1.Voltage of line
2.max fult current
Is This Answer Correct ? | 14 Yes | 3 No |
Answer / p l narayana
circuit breakers are selected in kva which can calculated
from the fallowing equation
KVA Rating=3^0.5*phase voltage*short circuit current*1.25
Is This Answer Correct ? | 2 Yes | 5 No |
electrical engineering giving priority for insulators rather than conductors, why ?
what will happen if i connect 12 volt battery with 24 volt battery charger.
What is difference between miniture circuit breaker and module case circuit breaker up to 63Amp.
trasformer ratting
Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of current?How can I calculate also when I have loads in KW?
Why do we mostly prefer to generate and distribute electricity in 3 phase and not in 4 phase or 5 phase?
How earth resistance reduses by pouring water coal and salt?
how to can we synchronize different capacity of DG sets.60kva& 250kva?
What is maximum AC & DC transmission voltage in India? and where?
plz explain the auot-reclosing circuit in electrical engineeing
what is 33 /11kv transformer bdv
My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help