for testing busbar (33kv) hi-pot .whether we can apply DC r
not.and what is the test volt for that .explain
Answers were Sorted based on User's Feedback
Answer / senthil kumar
we can able to test ac or dc. thats manufactures chosen.in ac hi-pot leakage current will be more(mA).but DC hi-pot leakage current will be less. but dc voltage charge the capacitance. in ac hi-pot we are applying 2V+1X 0.8 in dc hi-pot 2V+1X1.414X 0.8.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / vijay
Yes, we can.
For test voltage we have to apply 80% of factory test
voltage i.e. 80% of 70 kv ac (factory test voltage) =56 kv
for 1 min.
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / shaikh
For 33KV Ac Busbar testing, we can apply 5.0k (5000v)DC for
1-3 mints.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / ashish
For Testing Busbar 33 Kv ( HI-POT ) We Have To Apply the (
1.732* 33000)DC Volt for 3 min.
| Is This Answer Correct ? | 9 Yes | 18 No |
What is the function of isolater
4 Answers Getco, Gland Pharma,
Can we use HRC Fuse inplace of Semiconductor fuse?
Why the pointer of earthing of 3 pin top is made thick and long compared to the phase and neutral pin ?
tube light how its working.,?
what is the load amp of a 2 hp single phase motor?
What is the tube exial fan?
how can we determine size of a cable by knowing the kw or current rating of a load?how can we calculate the resistance box of a slip ring motor?
assume we are put both df/dt and vector surge relay in same bus the df/dt relay setting is +5 hz an -5HZ. we want operat the vector surge relay before the df/dt how i calculate the setting of the vector surge relay.
Why does The speed of motor used in elevator remain constant irrespective of load??
sir,in our plant we r using SATEC PM172E power reading meeters in HT panel side it is monitoring the MB data smart viewer(sever).but last one week we did not get readings inthe server only available in meeter.tell me how communicate meter and server. and also what steps we take for checking.
in elevator industries , how to calculate the required KVA for the elevator (elevator spec- 40A module , motor of 13.5KW, 20A)
1 Answers DLF, Tata Steel Limited,
what is the diff. b/w balanced and unbalanced load..?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)