for testing busbar (33kv) hi-pot .whether we can apply DC r
not.and what is the test volt for that .explain
Answers were Sorted based on User's Feedback
Answer / senthil kumar
we can able to test ac or dc. thats manufactures chosen.in ac hi-pot leakage current will be more(mA).but DC hi-pot leakage current will be less. but dc voltage charge the capacitance. in ac hi-pot we are applying 2V+1X 0.8 in dc hi-pot 2V+1X1.414X 0.8.
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / vijay
Yes, we can.
For test voltage we have to apply 80% of factory test
voltage i.e. 80% of 70 kv ac (factory test voltage) =56 kv
for 1 min.
Is This Answer Correct ? | 11 Yes | 6 No |
Answer / shaikh
For 33KV Ac Busbar testing, we can apply 5.0k (5000v)DC for
1-3 mints.
Is This Answer Correct ? | 3 Yes | 10 No |
Answer / ashish
For Testing Busbar 33 Kv ( HI-POT ) We Have To Apply the (
1.732* 33000)DC Volt for 3 min.
Is This Answer Correct ? | 9 Yes | 18 No |
what condition there autotransformer will fail?
Our Alternator nameplate specifies a power factor of 0.8. When the Alternator is on light load, the bus bar voltage rises to 11240 volts, whereas the standard value is 10500 volts. Is it ok to increase the power factor to 0.85 or 0.9. I am afraid because the power factor on the name plate is only 0.8 ?
why is a power transformer used only occasionally?it is used to step up at generating stations?and that needs to be done all day long !!!!!!!
how much Watt can we fully load a transformer
Why the vector group of excitation transformer in static excitation system is Dy5?
230v AC & 230V DC which is more dengerous for getting a clectric shock between this two voltage?
Why do we need interlocking in a HT metering or Ring main unit switchgear?
what is stper motor.what is its uses
what will be happen if we apply D.C supply to the transformer
what is mean by tan-delta tap in the potential transformer??
what happen "when Dyn11 is parallel operation with Dyn1"?
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors