I want Primary side delta and Sec side Star connection
transformer . but i have received Star - Star
transformer ,shall i use the same transformer by giving the
only 3 ph on Primary side without Neutral connection on the
Starpoint.
Answers were Sorted based on User's Feedback
Answer / ram niveth
offcourse we can use it if we didnt consider the clock
position ie, phase displacement in primary side.
but the condition is Neutral should not be earthed in
primary side .secondary neutral must be earthed
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / karthikeyan
definetly you should reconfigure your primary winding of
the Y/Y to D/Y as per requirement. or else you have to
brought out the neutral point of primary starwinding of the
now existing Y/Y transformer.Hence you can avoid unbalance
3 pashe current by availing neutral star point which will
balance the system. and one morer thing is that you should
earth the star point of the primary winding.
| Is This Answer Correct ? | 4 Yes | 10 No |
Answer / dolphinopera
in transformers the
starting and finishing
end of the phase
windings are brought
out. hence you can
connect the windings
either in star or in
delta. another
important thing, if the
star winding is used
without neutral there
is a possiblity of
damage of winding.
| Is This Answer Correct ? | 5 Yes | 12 No |
for star delta connection,,why the contactor star not burn,when red,yellow and blue cable is looping.
2 Answers Mahindra Water Utilities,
time constant of RC series circuit?
What is the meaning of TRI Vector meter?
7 Answers ABB, Excel Power Switchgear,
why in an industry; machine having rated 200 h.p stopped after power factor is maintained above 0.97 lag by control panel in view-of energy saving
a solenoid of inductance 250mH and resistance 10ohm is connected to a battery. the time taken for the magnetic energy to reach 1/4th of its maximum value will be?
Why does the rotor rotate?
1 Answers Machino Polymers, OPTCL,
We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.
why insulators are colured in brown only?
why electron produce magnetic field when it is in motion?
difference between synchronous reluctance motor and switched reluctance motor
there are 3 transformers each of 1500 kva and one transformer of 1000kva for a 11 floor building . total otgoing kw is 4066 kw. i need an extra 260 kw .is there any provision for that? what is the max kw that can be connected with these transformers?
What is earth fault?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)