Answer / ram niveth

offcourse we can use it if we didnt consider the clock
position ie, phase displacement in primary side.
but the condition is Neutral should not be earthed in
primary side .secondary neutral must be earthed

Is This Answer Correct ?    9 Yes 2 No

I want Primary side delta and Sec side Star connection transformer . but i have received Star - St..

Answer / vinod

Main reason to use Delta in primary side is to reduce/Eliminate harmonics in primary side whereas star winding will not eliminate.

Is This Answer Correct ?    0 Yes 0 No

I want Primary side delta and Sec side Star connection transformer . but i have received Star - St..

Answer / ssnslm

we can use the tr. in delta/star by disconnecting the
primary side winding teminals of each phase and reconnect
in delta in the primary side.

Is This Answer Correct ?    3 Yes 7 No

I want Primary side delta and Sec side Star connection transformer . but i have received Star - St..

Answer / karthikeyan

definetly you should reconfigure your primary winding of
the Y/Y to D/Y as per requirement. or else you have to
brought out the neutral point of primary starwinding of the
now existing Y/Y transformer.Hence you can avoid unbalance
3 pashe current by availing neutral star point which will
balance the system. and one morer thing is that you should
earth the star point of the primary winding.

Is This Answer Correct ?    4 Yes 10 No

I want Primary side delta and Sec side Star connection transformer . but i have received Star - St..

Answer / dolphinopera

in transformers the
starting and finishing
end of the phase
windings are brought
out. hence you can
connect the windings
either in star or in
delta. another
important thing, if the
star winding is used
without neutral there
is a possiblity of
damage of winding.

Is This Answer Correct ?    5 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?

1 Answers  


What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?

1 Answers  


What is an Air COmpressor

0 Answers   DLF,


how to calculate the earth fault current

0 Answers  


In a voltage-controlled current source A A current booster is never used B The load is always floated C A stiff current source drives the load D The load current equals Isc

0 Answers  






Why DG self motor winding burnt out?

1 Answers   Aegis,


what is the string efficiency

1 Answers  


What is transient Phenomenon?

0 Answers  


Hi, We facing one similar problem in our computers i.e we are newly constructed our design department after that shifted our computers but our computer desktop screen is vibrating. we are conducted our electrical maintainance person he told that is UPS problem, then we changed the UPS also again we are facing that problem in that room only. then we put lcd monitors that problem is solved. But in other monitors why the computer desktop screen is vibrating please give a suggestion to me. Regards, Raju.N.G

10 Answers  


can we say current flows inside an atom as electron moves inside an atom?

7 Answers   Vedanta,


A 3 phase motor operating off 415V system is developing 20Kw at an efficiency of 0.77 and power factor of 0.73. determine:- a)the line current. b)the phase current if winding are delta connected. c)the phase voltage if winding are star connected.

1 Answers  


Define phase lag and phase lead?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)