why in three phase 440 circuit in all phase current is
almost equal L1-35 A,L2-34 A ,L3-31 A but in nutral when i
check with clamp meter it shows 25 A?
Answers were Sorted based on User's Feedback
Answer / kiran
Principle is vector summation.
Ir + Iy + Ib = 0
and not arithmatic summation.
Since neutral current is substantial 25A, the three RYB
vectors are not 120 degree apart. Means powewr factor in
each phase differs drastically. Thats why though there is
no much difference in RYB current, neutral has substantial
current.
Is This Answer Correct ? | 18 Yes | 2 No |
Answer / amit
In balance condition neutral current is zero. Flux in all
three phases are in addative nature.
flux in R + flux in Y + flux in B = 0(zero)
but in your case it is different because of differnt
currnet in phases, which will affect and cause a unbalance
condition, will produce a flux in neutral and current
flowing through neutral. But in your case it is 25A which
is to much unbalance condition.
Take once again reading.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / rajesh siwach
valve of currents and voltages depend upon the manner in
which the 3 phase system connected,either in star
connection or in delta connection
Is This Answer Correct ? | 1 Yes | 4 No |
What is the estimated total hydropower potential of india?
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
can we calculate the diameter of the cable by its cross section?
what will happen if i connect the buchholz relay in reverse direction.
what is the differance beetwen installation and errection ?
What precautions we have to take while handling electrical equipments?
how is working the APFC when varying the load?
what is use of reactive power in ac ckt.
What will be the full load current of 60KVA UPS. Suggest for this formula.
how to test an MCB