why in three phase 440 circuit in all phase current is
almost equal L1-35 A,L2-34 A ,L3-31 A but in nutral when i
check with clamp meter it shows 25 A?
Answers were Sorted based on User's Feedback
Answer / kiran
Principle is vector summation.
Ir + Iy + Ib = 0
and not arithmatic summation.
Since neutral current is substantial 25A, the three RYB
vectors are not 120 degree apart. Means powewr factor in
each phase differs drastically. Thats why though there is
no much difference in RYB current, neutral has substantial
current.
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / amit
In balance condition neutral current is zero. Flux in all
three phases are in addative nature.
flux in R + flux in Y + flux in B = 0(zero)
but in your case it is different because of differnt
currnet in phases, which will affect and cause a unbalance
condition, will produce a flux in neutral and current
flowing through neutral. But in your case it is 25A which
is to much unbalance condition.
Take once again reading.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / rajesh siwach
valve of currents and voltages depend upon the manner in
which the 3 phase system connected,either in star
connection or in delta connection
| Is This Answer Correct ? | 1 Yes | 4 No |
what is a relay?
How can get C license i am complete I.T.I electrician trade and 10 years experiance this field and i complete the dee from ksou by distance mode of this year.ksou means karnataka south open university but i want Tnelb license
What is a surge supressor why its is used in synchronous generators
why T/F winding temp measurement cts are odd secondary current ie,109A/1.2A/1.4A?
0 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva.how much each tranformers share the load????
6 Answers TNEB Tamil Nadu Electricity Board,
why earthing is not required on transformer prymary winding side ???
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
the resstance of a thermistor is 5000 ohm at 25degreeC and coefficient is .04/degCel. A measurement with lead resitance of 10 ohm will cause an error of
Do you know the alignment of a motor?
What is the basic principal of Diesel genarator?
3 Answers Juniper Networks, MRF,
What is the previous name of Cox's Bazar
H.t motor 6600 volt to same motor lt supply 440volt supply applyed to h.t motor to effect....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)