in the farm,water tank of 8000 litter capacity situated in 12 meter above.Farm owner want to lift 7000 litter of water within 7 minute to water tank of 12 meter above.which motor having HP rating is suitable for pumping??
Answer / alexey
P=dA/dt;
A=F*S=7000[kg]*10[m/s^2]*12[m]=0,84[MJ];
P=0.84[MJ]/(7*60[s])=2[kW]
P=2[kW]*1,34=2.68HP
Approximately 2.68HP motor will be enough
Is This Answer Correct ? | 0 Yes | 0 No |
how the characterstics of control valve being done
What do you mean by boost voltage in case of battery charger?
can someone explain that how the speed of the protection system affects the fault level calculation?
corona happens more in ac or dc?
What will be the current if the resistance total in a series circuit doubles?
What are the Safety Steps While Inspection the LT Panel.
What will be the excat cable specification in Sq MM...please find the details below.... Induction Motor HP:55 Amps:70(starting Amps),45(Running Amps). Volts:415
what does the word synchronous mean in 'synchronous machine'
how the testing of CT OF 400/200/100 done in33/11 kv s/s
what are the range of memory address in plc for L&T lx7 4A
I have two AC generators, the first rated 2680KVA for 380V/4345A/pf:0.7 and the second rated 3461KVA for 5500V/363A/pf:0.8. I want to parallel the two generator to a bus. The second generator passes through a transformer to down the voltage to 380V and a part of its power goes to another bus so that it's only a part of the total power of the second generator taht goes to the considered bus. I have two Basler DECS100 AVR regulator. How can I make the synchronization ? What others equipments must have ?
Transfer function is == ? a. Mathematical model b. System with no physical structure c. Can be calculated through differential equations