Answer / faizan
For cable selection we need supply voltage,load current and distence between source to load end ,then we can choose the size of cable and also it depends on meterial of cable,( cu/alu )..
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pratap
70 ton=245280watt
I=245280/1.73x440x.8
=402 Amp
cable size 400sq.mm(3 phase +neutral)
| Is This Answer Correct ? | 2 Yes | 4 No |
WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK
What is stacking factor? What is its approximate value?
what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine
Explain Creepage Distance of Insulator
What is the actual calculation for transformer short circuit test?.
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES ?
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
Mention what are the different colors on wires indicates?
What is meant by Low Resistance Cable and High Resistance Cable.
Difference between transmission line and cable?when ever a large water channel has to crossed it is easier to use cable then transmission line why?
what is power load and lighiting load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)