we want to feed 3 phase supply to 70 ton AC load.what will be the size of (3 phase)cable require.
Answers were Sorted based on User's Feedback
Answer / faizan
For cable selection we need supply voltage,load current and distence between source to load end ,then we can choose the size of cable and also it depends on meterial of cable,( cu/alu )..
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pratap
70 ton=245280watt
I=245280/1.73x440x.8
=402 Amp
cable size 400sq.mm(3 phase +neutral)
Is This Answer Correct ? | 2 Yes | 4 No |
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
Name quantities which are not transformed in the tranformer.
whay we used silica gel in Transformer
Why neutral is used in electrical system?
What is frantic effect?
what is the min and max dc voltage for a dc system (110vdc)
what is the installation process for lifts
how to modify DOL control panel into Delta Y connection?
Which are resistive loads & which one are inductive loads : Refrigerator, Split air conditioner, ceiling fans, well pump, fluoresecent bulbs, T.V, CRT Monitors, Adsl Routers, C.P.U, Printers, Deep Freezers, Speakers, DVD Players, Microwave oven etc. ? Output Power for these Appliances Would be same like this : P = V * A * P.F Or would be changed ? thanks
what is the working and construction of generator
how to give earthing in plain?
If NO contact of relay gets supply from other sources or other part of circuit and at a time relay coil activates,then current will flow in which direction & will it cause to damage relay??