If we know the load for generator in KW then how it will be
change to amps and also if we know the load in amps how it
will change in KW and what Generator is good for
that...suppose load is 500 amps 3phase......??
Answer / ram t shelke
Techanically speaking , Generator is a DC machine i.e an
machine used to supply DC power.but you are saying that it
is a 3phase machine . so you might be talking about
alternator.
if you know the value of generator current , it can be
expressed in terms of KW provided one should know the
terminal or O/P voltage of generator.use following equation
for the required convertion.
KW = 3* TERMINAL VOLTAGE per phase (V) * RATED CURRENT
per phase (A) * power factor/1000
On the other hand , if you know KW out put, one can
calculate corresponding current by following equation
current per phase(A) = kw rating*1000/ 3* voltage per phase
(V)* power factor
| Is This Answer Correct ? | 0 Yes | 0 No |
Two alternators say 1 & 2 are poised to parallel operation. But at the time of paralleing alternator 2 gets out of the system by tripping Earth fault relay. Please send me reply why this is happening?
wat s reactive power.... how could it be compensated.....
How to test and satisfy the conditions of the vector group YNd1 for power transformer?
why scott connection is done why not two phases are directly picked at the output of 3 phase transformer??
What the reson for frequant instantaneous ground over current fault in our sync. Generator... 15 triping in 24 hr...
1 Answers HCPL, Jhunjhunwala Vanaspati Jhoola, Regen Powertech,
In directional earth fault protection for generator, one core balance CT is for residual current, what other CT is for, which is placed on neutral?
what will happen if the connections of protection ct reverse? will it burn the ct?
What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?
Here iam a question with SYNCHRONIZATION PANNEL related issue, as i want to design a SYNC.pannel board iam giving the 2 nos of 1MVA Generators to sync pannel , then what wil be the out put of the sync pannel, whether it wil be one cable coems from the sync panel or two cables.. as iam using two transformers to meet my load demand, so pls clear me whether two cables comes from sync panel to connect to transformers or only one cable
What is function of condenser in fan?
i want some interview related questions with their answers which can help for attend the interviews...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)