IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT
CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL.
AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE
PROVIDED
Answers were Sorted based on User's Feedback
Answer / sudhakar g
First you have to caluclate the load of the T/F i.e
KW=KVA*p.f
KW=500*0.8=400KW
I=kw*1000/1.732*415v*0.8
I=696.74 A
Based on these we can choose the Cable size ....
suppose the LT AL cable of 3.5c x 400 sqmm will give 530 A
of polycab....if we go for two runs of 400sq.mm means it is
good and the breaker size we will go for 800A ACB bresker
means it is good....
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 17 Yes | 13 No |
what is the thumb rule or formula for cable size and current ratings
my N-P 230 VAC at 3 wires but i haven't any voltages at phase to phase whither my supply is 3 phase, why i haven't received these line to line voltages ?
cb used in railway applications is?
Explain the operation principle, advantages and disadvantages of the following converters: a) A 12 pulse converter b) A Switch-mode inverter c) A thyristor inverter
for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single phase.why
WHY THE COLOUR OF TRANSFORMER IS GREY ?
If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board
What is the formula for calculating no-load current?
what is differnce between grounding and earthing or both are same?
Which motor is 3.3 or 11kV more reliable, in terms of efficeancy,maintenance, reliability.
0 Answers Megatron Solutions, TCL,
Why we are use 11KV / 22KV / 33KV / 66KV / 110KV / 230KV / 440KV this type of ratio. why cant we use other voltage ratio like 54KV / 99KV et.,
8 Answers College School Exams Tests, Hino, ITC Infotech, Reliance, UPRVUNL,
WHAT IS THE DIFFERENCE BETWEEN RESISANTANCE AND IMPEDANCE IF IMPEDANCE IS MORE THAN RESISTANCE AT SAME VOLTAGE CAN WE HAVE RELATION DERIEVED BETWEEN THEM
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)