IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT
CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL.
AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE
PROVIDED
Answers were Sorted based on User's Feedback
Answer / sudhakar g
First you have to caluclate the load of the T/F i.e
KW=KVA*p.f
KW=500*0.8=400KW
I=kw*1000/1.732*415v*0.8
I=696.74 A
Based on these we can choose the Cable size ....
suppose the LT AL cable of 3.5c x 400 sqmm will give 530 A
of polycab....if we go for two runs of 400sq.mm means it is
good and the breaker size we will go for 800A ACB bresker
means it is good....
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 17 Yes | 13 No |
WHAT IS THE FORMULA FOR CALCULATING CURRENT RATING(DIRECT IN GROUND OR AIR) OF ARMOURED(XLPE) CABLE OF 4C,16Sqmm?
WILL THE PERCENTAGE IMPEDENCE FOR A ONAN TRANSFORMEER BE THE SAME COMPARED TO ONAF TRANSFORMER OF SAME RATING???
kva/kvr
what is ripple ??? what is harmonics ?
at the time of starting back emf of a motor is zero.so how can it will start to run??
what is the meaning of 16/20 mva of transformer
what is raw power & normal power
how capacitor buield up the voltage
wat do knw aboot circuit breakers ?
how to write program by ladder logic in case of PLC operation
how we sesign the transformer give some specifion regarding design of transformers
why the check zone and main zone are used for Busbar Protn. scheem?