how much the voltage & resistance should be ,between earth
& neutral points.?& why?
Answers were Sorted based on User's Feedback
Answer / sheikh
i think voltage b/w earth and neutral should be zeero.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / hemant
voltage btwen earth and nuetra must be zero, then and then
only its give close path to nutral for single phase or 3
phase 4 wire system if not then its difficult to drive
equipment on such circuit.
| Is This Answer Correct ? | 6 Yes | 0 No |
voltage and earth resistance 0 to 3 volt acceptable in india
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / koti
voltage should be less than 5 volts (to avoid mal-functioning of controls) and resistance should be below 50 milli ohms.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pradyumna chandra panda
the resistance b/w earth and neutral 1.8 kohm is accepted and in 3phase supply voltage b/w earth and neutral 3v to 20v is accepted.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / jayasen jena
the voltage mot be less then 3 & resistance 100 milli ohoms
| Is This Answer Correct ? | 0 Yes | 0 No |
If the (Motor control center)Panel work on field the relay used in panel in the case this will be damage and no indication provide on panel.fault occur in panel and MCB will not trip. how happen the relay damage in panel and what effect of panel.
What current position are you holding in your current company?
what is working process of star delta controlling circuit ?
There is two transformers of 2MVA & 3MVA, which transformer is located at the sending end & which is at receiving end. why?
Please tell me what is the difference between online UPS & OFF line UPS?
what are the importance of earthing?list different types of earthing.
How many earthing pits required for diesel generator set ? Why ?
for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single phase.why
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
HOW CIRCUIT BREAKER RATING CALCULATED?WHAT ARE THE PARAMETERS CONSIDERED?
what is the disadvantage of leading power factor...why can't we use it (pf=0) for a long period of time?
Which standard i will refer for size of earthing conductor for equipment? (Eg:415V Switchgear, MCC, DB shall be 50x6mm GI flat)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)