Sq. root of ma-4/16*max. flow,
0% = 0 mmh2o
25% = 12.5 mmh2o
50% = 35.25 mmh2o
75% = 37.5 mmh2o
100% = 50 mmh2o mmh2o
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / che-daniel cabardo
the formula is Q=k(square root percent of 0%,25% and so on.)
therfore k=10,constant..
for example range is 0 to 50 mmh2o
the span is 50 mmh2o.
Q=10 multiply sq. root of 25%= 50%
from the formula: %(span) + LRV
So:
0% = 0 mmh2o
25%= 25 mmh2o
50%= 35.3 mmh2o
75%= 43.30 mmh2o
100%= 50 mmh2o
Is This Answer Correct ? | 4 Yes | 7 No |
how to calibrate Necleuonic level transmitter.?
it is possible to check the fail safe condition in pressure transmitter. if possible how?
why we are using 4-20ma why cant we use 4-40ma
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
What is cv of control valve
Operational amplifiers
PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS
To find closed tank level by DP transmitter , how to findout its range.and insomeplace they using range like - 1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit they range for minus and plus.and why?
How can we use feedback signal frm rtd for monitoring and in dcs for controlling ,then which type of rtd is sutaible 2 , 3,4wire and why ?
what is Instrument Schedule, and what it is mainly used for?