Sq. root of ma-4/16*max. flow,
0% = 0 mmh2o
25% = 12.5 mmh2o
50% = 35.25 mmh2o
75% = 37.5 mmh2o
100% = 50 mmh2o mmh2o
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / che-daniel cabardo
the formula is Q=k(square root percent of 0%,25% and so on.)
therfore k=10,constant..
for example range is 0 to 50 mmh2o
the span is 50 mmh2o.
Q=10 multiply sq. root of 25%= 50%
from the formula: %(span) + LRV
So:
0% = 0 mmh2o
25%= 25 mmh2o
50%= 35.3 mmh2o
75%= 43.30 mmh2o
100%= 50 mmh2o
| Is This Answer Correct ? | 4 Yes | 7 No |
what pressure transmitter?
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?
What is 3 element control system
kindly tell where orifice,nozzle,air foil,ventury used in flow measurement?
Why went
When cryogenic control valve will be applied?
why we use npn sensor in vibration monitoring system
what barrier is used in process industry.
3 Answers ADMA OPCO, Process Industries,
what is the difference between venturi and orifice meters?
what is the conversion factor for nm3 to kg/hr in air flow
WHEN DO WE GO FOR FMCW TYPE RADAR & PW TYPE RADAR ?
How is SmartPlant Instrumentation related to INtools?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)