how will do square root transmitter calibration
Answers were Sorted based on User's Feedback
Sq. root of ma-4/16*max. flow,
0% = 0 mmh2o
25% = 12.5 mmh2o
50% = 35.25 mmh2o
75% = 37.5 mmh2o
100% = 50 mmh2o mmh2o
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / che-daniel cabardo
the formula is Q=k(square root percent of 0%,25% and so on.)
therfore k=10,constant..
for example range is 0 to 50 mmh2o
the span is 50 mmh2o.
Q=10 multiply sq. root of 25%= 50%
from the formula: %(span) + LRV
So:
0% = 0 mmh2o
25%= 25 mmh2o
50%= 35.3 mmh2o
75%= 43.30 mmh2o
100%= 50 mmh2o
Is This Answer Correct ? | 4 Yes | 7 No |