There is an equipment to locate fault ,or you have to resort to loop test
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / santoshvarma
You can find the faulted location with the help of multimeter.
Measure the capacitance at both the ends,between faulted
phase with respect to earth.
For one end if it is C1 and for other end it is C2. And
total length of cable is L and Capacitance is C.
Then by using the below formula, you can find the faulted
location
LC=L1c1+L2c2
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rax
transverse nature of waves is utilised to find the location of fault.when a high dc voltage is superimposed on a signal it becomes a wave. now this wave is given a velocity of 67.5meters/microseconds for 11kv cable and 80 meters/microseconds for 33 kv cables. at the open end the voltage is doubled and the wave is reflected .the time taken by this wave to reach the source is noted and the distance is calculated.
Is This Answer Correct ? | 1 Yes | 0 No |
What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.
For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?
How vaccum is formed to create a vaccum interrupter or anything related with vaccum?
explain the mode of metal iranafer in Co,welding
what is effect of length of air gap on performance of dc motor and generator?
In more then 1 phase bulb will glow are not?if yes then how it will glow?
What will happen if 40W and 60W Bulb is Connected in Series.
state the working of discharge lamp?
if we convert watt into kva,which one formula use by us,pls tell me?
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
when voltage increases current decreases & vice versa why it is so?
what is difference between earth and ground?/
3 Answers Sree Rayalseema Green Energy Limited SRGEL,