If the on Of the DO module is off in the System cabinet,
then what is the Procedure to check weather the Module is
working or not.
Answers were Sorted based on User's Feedback
Answer / a k gunjariya
If DO Module is OFF in system cabinets:
1.) Check status of the 24 V Power Supply (power supply LED
on the module)
2.) IF No LED is glowing then module is not getting power
supply.
3.) if power supply led is glowing then check any of the
Digital Output signal by simulating input.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / ahmed samy
Make forcing from PLC programming software to any output Channel in that DO, if output is on, LED is on means module is ok, otherwise it's faulty.
Other idea, is to replace module with similar one in the rack, if it's still off in second position that means it has a problem
Is This Answer Correct ? | 2 Yes | 0 No |
please tel me the calibration of pneumatic controler.
Definition of reverse and acting controllers:
1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?
3 Answers EI Electrotechnical Institute,
in mass flow meter what is drive friquancy ?
What are the cable come out from the paddle type flow sensor.and how is further connections
Define magnetic flow meter and mass flow meter.
Hi Frnds , If Suppose 1 Pair cable of 1.5 sq mm is used for Transmitter and instead of 1.5 sq mm if i used 0.5 sq mm cable will the resistance change will occur and does it affect our transmitter reading. plz mail ur answer to ntnkamble@gmail.com plz immediately mail ur reply
how to commission furnace ( water heater)
Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?
what is the name of thermocople element cable from field to pannel end?
why we use 24 vdc in instruments mostly?
Somebody ask me how many size of control valve what is mean of control valve size?