Describe the method of Plate Earthing.
Plate earthing provids using copper plate (450mm x 450mm x
6mm). The area of the copper plate is high causing high
earthing value (Low resistance).
Instaling Method: The copper plate at the depth of 2 Mtr or
3 Mtr. The centre support provides using 40mm GI pipes,
funnel in top.The two numbers of 25mm x 3 mm copper flat
stamped from top of the GI pipe to copper plate to improve
the earth value. The salt, charcole to improve the
conductivity.
The materials using for plate earthing are as below:
1) Meshed Funnel
2) 40 x 300 x 6 mm copper earth pad
3) 25 x 3 Cu strip
4) Copper Rivit
5) 450 x 450 x 3 mm Cu plate
6) 8x25 mm bolt and nut with washer
7) 6x75 mm bolt and nut with washer
8) 40 mm GI pipe - 2.8 mtrs
9) 25mm dia x 200 mm length GI pipe with double end threaded
10) 40mm to 25 mm GI reducer
11) 1" Check nut(6mm thick)
12) Charcoal
13) Salt
14) 450 x 450 mm heavy duty SFRC chamber cover with frame
ersaravananp@gmail.com
Saravanan.P
| Is This Answer Correct ? | 6 Yes | 1 No |
IN A HT CABLES i.e. 1.9/3/3 kv, what is the meaning of 1.9 and 3.3.
In our domestic single phase line if you don't have a ground connection (earthing)how will you separately use earth in a specific power supply board.
why are you interested in joining in core company instead of joing in software company
how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.
What is differential relay ? where it can be used?
1 Answers Scope International,
Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV
what happenes if the core of the transformer saturates?
explain why the secondary terminal of current transformer should not be lift open circuited.
1.ZEBRA conductor(large size) 2.KUNDHA conductor( small size ) 3.panther conductor(very small ) 4.lepard conductor (very very small)
WHY PROTECTION CT IS USED NEXT TO METERING CT?
Is it possible to connect a dYN1 transformer in parallel with a YNd11 transformer.
what is residuel magnetism. and how order lead acid batteries for 24 volt. emergency lighting system.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)