How to convert KW to KVA or KVAR OR kvar/kva to kw?
Answers were Sorted based on User's Feedback
Answer / avvkishore
KW to KVA - KW/0.85=KVA
KVA to KW - KVA*0.85
| Is This Answer Correct ? | 142 Yes | 24 No |
Answer / manish2march@gmail.com
KW=KVA COSINE OF ANGLE BETWEEN VOLTAGE AND CURRENT.
AND
KVAR=KW TAN OF ANGLE BETWEEN VOLTAGE AND CURRENT
| Is This Answer Correct ? | 61 Yes | 17 No |
Answer / shivanand
KVA=KW/cos of angle b/w v and i
KVAR= kw*tan of angle b/w v and i
| Is This Answer Correct ? | 29 Yes | 9 No |
Answer / k.prakashchandra
In the load triangle ,to the angle between KW and KVA ,KW is
adjacent side , the opposite side is KVAR and hypotenuse is
KVA.KVAR is perpendicular KW
| Is This Answer Correct ? | 21 Yes | 4 No |
Answer / md.shahinuzzaman
KW=KVA COSINE OF ANGLE BETWEEN VOLTAGE AND CURRENT.
AND
KVAR=KW TAN OF ANGLE BETWEEN VOLTAGE AND CURRENT
| Is This Answer Correct ? | 22 Yes | 5 No |
Answer / harshad.p.s
KW= KVA*PF
If PF is 0.8
KW= KVA*0.8
If PF is 0.9
KW= KVA*0.9
| Is This Answer Correct ? | 20 Yes | 3 No |
Answer / ranjan muduli
KW TO KVA = KW*COS Phai
KVA TO KW = KVA*COS Phai
| Is This Answer Correct ? | 6 Yes | 23 No |
If any cable burnt how can we identify it burnt by high current of high voltage?
can u light up bulb with out useing neutral
What is meaning of DRU in gen.of AVR.
how i sync. the different size of generator.
difference between ceiling fan
24 Answers Altius Technologies, Raisoni, TCS, Uni Deritend,
why scott connection is done why not two phases are directly picked at the output of 3 phase transformer??
why do we use UPF watt meter in short circuit test of the transformer and LPF watt meter in open circuit test of the transformer
why the desirable efficiency for a motor is 60%, but in case of transformer, it is above 90%?
when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?
why a fan starts rotating in the reverse direction when condenser gets damaged?
We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)