How to convert KW to KVA or KVAR OR kvar/kva to kw?
Answers were Sorted based on User's Feedback
Answer / avvkishore
KW to KVA - KW/0.85=KVA
KVA to KW - KVA*0.85
| Is This Answer Correct ? | 142 Yes | 24 No |
Answer / manish2march@gmail.com
KW=KVA COSINE OF ANGLE BETWEEN VOLTAGE AND CURRENT.
AND
KVAR=KW TAN OF ANGLE BETWEEN VOLTAGE AND CURRENT
| Is This Answer Correct ? | 61 Yes | 17 No |
Answer / shivanand
KVA=KW/cos of angle b/w v and i
KVAR= kw*tan of angle b/w v and i
| Is This Answer Correct ? | 29 Yes | 9 No |
Answer / k.prakashchandra
In the load triangle ,to the angle between KW and KVA ,KW is
adjacent side , the opposite side is KVAR and hypotenuse is
KVA.KVAR is perpendicular KW
| Is This Answer Correct ? | 21 Yes | 4 No |
Answer / md.shahinuzzaman
KW=KVA COSINE OF ANGLE BETWEEN VOLTAGE AND CURRENT.
AND
KVAR=KW TAN OF ANGLE BETWEEN VOLTAGE AND CURRENT
| Is This Answer Correct ? | 22 Yes | 5 No |
Answer / harshad.p.s
KW= KVA*PF
If PF is 0.8
KW= KVA*0.8
If PF is 0.9
KW= KVA*0.9
| Is This Answer Correct ? | 20 Yes | 3 No |
Answer / ranjan muduli
KW TO KVA = KW*COS Phai
KVA TO KW = KVA*COS Phai
| Is This Answer Correct ? | 6 Yes | 23 No |
Discribe type of fault in DOL and stardelta startor.
the inertia constants of two machines are respectively 30and 42 MJ per MVA.when the change in frequency due to change in load in first machine is 12 Hz,the change in second machine frequency will be?
in dc shunt motor if field winding is shorted then
how step up transformer step up the voltage and what is the reason behind it?
Transmission lines usually use a.3 phase b.2 phase c. Single phase
What is the formula to calculate the size of Aluminium and copper cable?
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?
which is more dangerous A.c or D.C?
URGENT PLEASE//////////A WORK SHOP IS HAVING A 100 KVA TRANSFORMER 11KV/415 VOLTS, AND THE CONNECTED LOAD OF THE WORK SHOP IS 80 KW WITH INDUCTIVE LOADS, LIGHTING LOADS,ETC., HOW MANY EARTH ELECTRODES ARE NEEDED AND WHAT IS THE EARTH RESISTANCE OF EACH EARTH ELECTRODE AND COMBINED EARTH RESISTANCE in normal soil. AT 11 KV SIDE AND AT LT SIDE. HOW TO CALCULATE.
the parts of transformers ?
1 Answers Bhel, Facility management,
Why CT secondary is grounded?
Hello Friends, How can we recognize the CT Star Point is S1 or S2 in case of Electro Mechanical Relays and what is meant by Restraining coil in relays and what is the purpose of that.. thank you in advance..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)