I have 30KW Motor Starter Panel, System voltage is 480V, So i have to convert voltage 480 to 220V to give the contactor coil. How i can select control transformer, Which rating transformer i can use this panel, what is the procedure, please tell me.
Answers were Sorted based on User's Feedback
Answer / santhosh(adityabirla group)
u know ur motor kw and supply voltage, first u have to
calculate ur full load amps,
KVA 480V
30 36A
45 54A
75 90A
now u have to select ur rated KVA trafo
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / santhosh(adityabirla group)
transformer selection calculation
A=KVA*1000/V*1.732
ex: ur amps:36
volts :480
calculate ur KVA
Ans:29.92
selact :30KVA
Is This Answer Correct ? | 2 Yes | 0 No |
why would the rotor rotate at sub synchronous speed against the direction of rotating flux when d rotor of 3 phase IM is connected to 3 phase balanced supply and the stator windings are shortcircuited ??
i seen a 132kv/11kv transformer,and thier is a sugar factorys 10MW EXPORT PLANT,MY QUESTION IS THAT WHEN THEY EXPORT ELECTRICITY THEY USE THE SAME TRANSFORMER AND THE CONNECT IT TO 132/11KV TRANSFORMERS SECONDARY SIDE CAN ANY ONE EXPLAIN IT.. THE TRANSFORMER IS OF KIRLOSKAR MAKE AND IT HAS TAP CHANGER.
Draw a Block diagram of TWO UPS systems connected in Parallel in Paralled mode?
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
what is %impedanece
How much load can be taken for chiller from 1500 kva transformer
what is earthing transformer? draw the winding dia.of earthing transformer.
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?
What are the uses of MCB & ELCB ?
Just a silly question but just to make my curious mind bac to normal - Why was not 67 and 67N relays built into a single relay as i have noticed that the R,Y,B CT wiring end up into the 67 relay while the common of the R,Y,B CT wiring end up into the 67N relay. Then it was better if a single relay was manufactured just like the distance relay (21). Another question i would like to ask is - how do we know where the 67 and 67 N relay has to be placed.why is it not placed at the transformer bay? In the substaion that i am working -i have noticed that it is placed between a breaker and a common double bus bar and this line bay is connected to another substation at a remote place which is furthur connected to a load. B U S______CT for 67 & 67N ______Breaker _____ remot s/s. B A R
What are Directly Exited Generators?
if we give connection of 100watts bulb through a single phase energy meter ,the disc of a meter rotates why it happens?