I have 30KW Motor Starter Panel, System voltage is 480V, So i have to convert voltage 480 to 220V to give the contactor coil. How i can select control transformer, Which rating transformer i can use this panel, what is the procedure, please tell me.
Answers were Sorted based on User's Feedback
Answer / santhosh(adityabirla group)
u know ur motor kw and supply voltage, first u have to
calculate ur full load amps,
KVA 480V
30 36A
45 54A
75 90A
now u have to select ur rated KVA trafo
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / santhosh(adityabirla group)
transformer selection calculation
A=KVA*1000/V*1.732
ex: ur amps:36
volts :480
calculate ur KVA
Ans:29.92
selact :30KVA
| Is This Answer Correct ? | 2 Yes | 0 No |
how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???
Transfer of electric power from primary to secondary in a transformer takes place A electrically B magnetically C electro-magnetically D conductively
IN SINGLE PH TRANSFORMER IF LEKAGE IMPEDANCE DROP IS NEGLECTED ,THE FLUX IN THE MAGNETIC CORE and the lekage flux linking a winding are a)proportional to the applied v to the winding i respectively.
What is the different between buchholz relay and pressure relief device?
What will happen to the speed of synchronous machine subjected beyond the pull out torque? Are the behavior shown by rotor remains same for both the alternator and motor?
A.V.R maintains the voltage of a generator when it is in island mode but when the generator is synchronised with grid it maintenance the P.F,how it happens please any body explain it in detail.
The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current
Why cant we connect the motor output to generator and then generator output to motor ?
Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?
Is it required to lay GI wires along with GI/MS conduits from one point to another point though separate earthing cable is conncted from DB to Socket?
Which motor will you choose which can operate in both lagging as well as leading power factors?
why 2 phase is used in argc furnace? why 6 phase is used in converting machinery?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)