What are the tests carried out on transformer while testing
at sites?..Pls explain me in detail
Answers were Sorted based on User's Feedback
Answer / arpit sood
an important test is the tan delta test or the dissipation
factor test
This is carried out with the help of an automatic scherring
bridge to measure the capacitance of the insulation
this is a measure of the integrity of the insulation or the
life expectancy of the transformer
the value of the dissipation factor should be more than or
equal to 0.7
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / sadineni sreedhar
we are carried out the below tests
1)IR-insulation resistance
2)turns ratio test
3)winding resistance test
4)automatic capacitance and tan delta or dissipation test
5)short circuit and open circuit test
6)vector group test
| Is This Answer Correct ? | 3 Yes | 0 No |
Reversal of corrent feature in MCCB- What is reversalof current -explain broadly.
Define super node?
what do you mean by PF correction. A motor is rated at 15 kw,415 volts, 0.7 pf and eff of 0.92. The powerfactor is improved to 0.98 by adding capacitors at the bus. calculate the current drawn by motor under full load condition before and after pf correction
Let's say I have 2 current carrying conductors C1 and C2 carrying currents of 5A and 10A. They are brought close to each other from a distance of infinity to a distance of 10cm away from each other - 1. What would be the values of current flowing in each conductor when (taking into account effects of interference of each conductor on the other) - a. The currents are AC b. The currents are DC c. C1 is AC and C2 is DC Please explain your answer with mathematical equations and formulas. Please specify the final numeric answer. Please make assumptions and clearly specify them.
What is PCCB?
if we convert ampers into kwh or mwh ,which one formula use by us,pls tell me?
What is the principle of Excitation.
HARMONICS ARE ALWAYS IN INTEGER LIKE 2ND OR 3RD HARMONICS,NOT IN FRACTION LIKE 0.5 HARMONICS.....????????
cc of scorpio?
If the battery is in charging condition means, battery is which type of load? Capacitive or Resistive load?
Dg pf .71 i am improve pf 0.80 what capacitor connected in dg how?
0 Answers AVT Natural Products, EMC,
what should be the no load current for 3 phase ac motors ranging from 5 kw to 1000kw?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)