Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
------------
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-tophase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the
phase-to-neutral voltage of the system.
·D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds.However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
| Is This Answer Correct ? | 5 Yes | 0 No |
Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-to phase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the phase-to-
neutral voltage of the system.
D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds. However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / john
HRG - High resistance grounded.
LRG - Low resistance grounded
| Is This Answer Correct ? | 2 Yes | 0 No |
Why is a thicker conductor necessary to carry a current in A.C.as compared to D.C. ?
what is buchholz relay?what is it used for?
8 Answers Engineers India Limited, NFCL,
We've 2 diffrent DG's with same capacity (500 KVA). Can we sync them ?
why the the electrical machine coil are damage ? How to prevent it?
what is the earthing condition between earth & phase.
why we are having many type of vector group in the transformer ,what is the use of it?
Why cpaciter opposes sudden changes in voltage?and how?
How to take vector group test for Ynd11 transformer.
why transformer measures in kva
What is the criteria for deciding whther fire wall is required between two power transformers
What is the diffrence between an ELCB(earth leakage circuit breaker) and RCCB(residual current circuit breaker)?which has higher degree of safety and why?
what will happen if capacitor bank is used in generation side?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)