Why HRG and LRG used beside transformer, what is the purpose
Answers were Sorted based on User's Feedback
Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
------------
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-tophase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the
phase-to-neutral voltage of the system.
·D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds.However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
Is This Answer Correct ? | 5 Yes | 0 No |
Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-to phase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the phase-to-
neutral voltage of the system.
D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds. However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / john
HRG - High resistance grounded.
LRG - Low resistance grounded
Is This Answer Correct ? | 2 Yes | 0 No |
how many test is necessary for 27mva transformer.
How to calculate the sag of OPGW during stringing???
why two windings are using in single phase AC motor
When we use 3 terminal resistor?
what is first ground fault & second ground fault. This is used in rotor protection of alternator.
what is function of rtu?
Explain why inductance of the iron cored coil changes with current?
What is the impedence of Transformer?
what is the application of dynamic Breaking resistor in inverter ? & How it works ?
1. How many types of mangers? 2.How many types of capacitors? 3.pls tell me normally types alternator problems?
how did the differential relay work to protect the power transformer
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks