what do you mean by earth fault in transformer?
Answers were Sorted based on User's Feedback
Answer / shailesh aggarwal
Basically Earth faults are caused if high fault current
flows through the neutral of the transformers. This type of
fault arises mainly in Star connected transformers.Earth
faults are specified in many categories:
1. Restricted Earth faults(Inside the zone HT/LT side of
trafo) Connection are done b/t Phase CT & Neutral CT of
tranformer)Indicated as REF(64)
2. Standby Earth Faults(Directly linked with neutral of
trafo)connection only done b/t neutral CT.Indicated as SBEF
(51N).
Both the protection give signals to the numerical relays
and cause the tripping as earth faults and directly trip
the transformer.
Thus in order to save transformers a proper earthing is
required whether solid or usong NGRs.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / nilkanth tailor
EARTH FAULT REQUIRE C.T.(CURRENT TRANSFORMER)..TO SENSES
IMBALANCE IN 3 PHASE..GENERALLY 3PHASE SYSTEM IS IN BALANCE
CKT...IF SINGLE OR MULTI PHASE WAS EARTHED..AND AT THAT
TIME IMBALANCE PRODUCED..CT WILL BE DETECT FAULT CURRENT
AND CIRCUIT BREAKER WILL BE OPEN...THATS CALLED EARTH FAULT
PROTECTION OF X'MER...
| Is This Answer Correct ? | 9 Yes | 6 No |
Is there any scope for an electrical engineer in MRF company......
What is resolution of a measurement?
why dc exicitaion used in ac motor....?
why do select 11000v rubber mat even we use only 415Volts
1 Answers Saint Gobain, Tata Steel Limited,
Why winding temperature ct placed in B-Phase of the transformers??
why transformers are put with supply for 24 hours before giving supplying to a locality?
While miss missed name platform fo electric motor how to calculate simple fourmul,?
what is slip rings in an induction motor&what is it's work.
when qty of cable being purchased is not sufficient according to the standard,what should the inspector do to ensure its quality according to the standard?
what is HVDC, what are advantages over conventional system?
hw to find transformer is in normal position? whether its in charged condition or not? except humming sound?
We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our electrical load . the issue is though we have Glanded the cable both the end also givan the earthing to the panel both the end we are facing a heavy sparking at the gland side. what could be the reason.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)