HOW THE AC GENARATOR CAN GENARATE REACTIVE POWER,HOW CAN WE
CONTROL IT.AND OTHER SOURSES OF REACTIVE POWER GENARATIONS
ARE WHAT.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Reactive of generator can be controlled if is connected to
grid/ network, by varying the excitation.If the gen
terminal voltage is higher than the grid voltage ,reactive
power is positive ( lagging) and the vice versa
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gopal manda
first of all i want to tell you that reactive power is use to create magnetic field in a coil.It can not consume but absorbed by inductor and provided by capacitor.
It can be controlled by the excitation voltage of synchronous machine.when machine's excitation is increase,reactive power also increase and vise verse.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bijoy
if we run it with it synchronous speed then its power factor
will be increase also its reactive power will be increase.
by controlling its speed we can control its reactive power.
| Is This Answer Correct ? | 1 Yes | 1 No |
what does work of electrical technician in industrial
What is the Difference between Power Swing and Out of Step?
Here iam a question with SYNCHRONIZATION PANNEL related issue, as i want to design a SYNC.pannel board iam giving the 2 nos of 1MVA Generators to sync pannel , then what wil be the out put of the sync pannel, whether it wil be one cable coems from the sync panel or two cables.. as iam using two transformers to meet my load demand, so pls clear me whether two cables comes from sync panel to connect to transformers or only one cable
Why the transformers are rating in KVA.?
What do you mean by a phase angel of instrument transformer?
how many single tension hardware are required on a double circuit transmission tower?
What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr
how to control the speed to switched reluctance motor
differentiate between c curve and d curve MCBS?
What type of input will the OLTC indicator will accept or what type of output the OLTC will produce to monitor it's position at remote location.
My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help
what is the burden?accuracy?Knee point voltage? what is the Alternator of PGM?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)