Answer / saran
Turndown ratio basically indicates the range over which a
transmitter will work accurately. For example, if a
transmitter can be calibrated to measure 0 to 1 bar, 0 to 2
bar, 0-20 bar etc. to maximum 0 to 50 bar, then you can say
that the transmitter has a turndown ratio of 50:1.
Is This Answer Correct ? | 25 Yes | 7 No |
Answer / faiyaz ahmad
Turn down ration is process or technique which is used to measure the inlet or out let flow of fluids.
Is This Answer Correct ? | 0 Yes | 2 No |
why we use -ve voltage in vibration monitoring system.generally we use 4 to 20 mA as output of instrument then why we use voltage in vibration
how is hazardous and non hazardous area classified?
2 Answers Bhel, Power Plant, Samsung,
How will you calibrate PID controller? explain with example.
0 Answers Jacobs, Sirte Oil Company,
What is open loop and close loop?
4 Answers L&T, Pearl Distillery,
What is mean by trim?
a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?
why does a transmitter o/o signal starts from 3-15psi or 4- 20mA?
A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar
Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line to get 20mA O/P by adjusting SPAN ?
What are advantages and disadvantage of the ac supply load cell?
How do you calibration D.P transmitter? ?
What are the types of valves?