IF we have three 30KW motor, these motors are connected in
DOL, star-delta and VFD respectively, what will be the fuse
rating for the above three?
Answers were Sorted based on User's Feedback
Answer / g.bhaskar reddy
IF MOTOR FUSE RATING IS 3 TO 4 TIMES OF THE MOTOR FULL
CURRENT.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / raymondraju05@gmail.com
30kw motor full load 54amps starting current upend on type of rotor like(single,double,deep bar cage) so single cage 4 to 5 times, double cage 3 to 31/2 times, deep bar 2 to 3 time at the time of starting. Now we can decide to witch of motor used as say above.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gak
30KW DOL FLC= 52.5A, 30KW FASD FLC= 31.5A So 63A Fuse for
DOL & 50A for FASD
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / sanduri ramesh babu
3-phase 30kw means 40.21Hp, so rated current is 60amps. We
can use 60amp rating.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / sudhakar
30Kw motor taken 60amp's so we arange 350amp's fuse rating
Is This Answer Correct ? | 1 Yes | 4 No |
I am an American living in Vietnam and I have recently gotten a refrigerator from Japan and it is rated for 100 vac, but the power here is 220 so I bought a voltage stabilizer it has a 1 kva output rating. Can you please tell me what the amperage is? I'm confused and without a working fridge.
what is advantage of providing taping on HT side?
How to calculate that clean water supply in one Day from 150 KLD STP?
1. What is differential relay? How it operates?
WHAT ARE THE DATAS REQUIRED FOR SCS SIGNAL LIST PREPARATION?
we want install 11KV generator to supply power 12km far from the power house.Load to be fed is 1MW.which conductor should we use and wat will be transmission line losses?
What is the diffrece between ACB & MCCB
Why DC exitation to AC Generator? Why not AC?
why we are not giving the zone 1 trip command to the master trip relay
What is meant by short-pitched winding?
how to write program by ladder logic in case of PLC operation
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?