difference between isolater and circuit breaker?

Answers were Sorted based on User's Feedback



difference between isolater and circuit breaker?..

Answer / ashoke

Both are used for isolating/breaking the circuit.Isolator is
used for breaking dead circuit and circuit breakers are used
for breaking live circuit.For an example A.B.switches are
isolators wheres O.C.B,V.C.B,SF6 etc.are circuit breakers.In
isolator there is no arcing due to operation for dead
circuit,so no arc quenching medium is required.But due to
live circuit there is arc quenching medium is necessary so
in circuit breakers the medium are like oil,vacuum,SF6
etc.The isolators are mainly used for protection purpose
isolation of circuit.

Is This Answer Correct ?    14 Yes 2 No

difference between isolater and circuit breaker?..

Answer / balram raturi

major diffrence is that isolator operates on no load &
circuit breaker operates on load

Is This Answer Correct ?    14 Yes 2 No

difference between isolater and circuit breaker?..

Answer / sagar kakade

Isolator is nothing but a switch which is used for just on
and off the circuit. Circuit breaker is also used for on
and off the circuit, but the major benifit of using circuit
breaker in place of isolator is to trip on major electrical
faults like, a) Earth fault, b) over load, c) Under
voltage / No voltage, d) Short circuit fault. and damage to
the human beings as well as the electrical machinaries like
transformers, HT/LT panels, HT/LT cables, can be prevented.

Is This Answer Correct ?    4 Yes 0 No

difference between isolater and circuit breaker?..

Answer / pillay

I just wish to add something to the above. As said isolators are
generally used to switch on or off an unloaded circuit.They are
usually manually operated but breakers are capable to operate on
their own or remotely during over current or earth fault or just
to break the circuit with the help of under voltage or no volt
coils. The important fact is they are designed to operate on
loaded condition.

Is This Answer Correct ?    3 Yes 1 No

difference between isolater and circuit breaker?..

Answer / chirag

isolater is off load devise and ckt breaker is on load load
device,ckt breaker operates on the signal given by relay
coneected with it, while isolater open manually.

Is This Answer Correct ?    2 Yes 0 No

difference between isolater and circuit breaker?..

Answer / vinoth

Isolator acts like switch and it does not have any breaking
capacity.. it is used for low rating

Breaker is also a switch but it have some breaking capacity
and withstands the fault current for few sec... it is used
for higher rating...

Is This Answer Correct ?    2 Yes 0 No

difference between isolater and circuit breaker?..

Answer / santhoo

Isolator ded circuit , circuit breaker live circuit

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

when we design electrical schemes of 11/.415kv distribution..wen and were should we show the relays??what is the function of it?for example..we place EFR Relay CT between transformer neutral link and transformer earth.Like this what are the other type of relays we should use?why?where?Explain please..Thank you

0 Answers   ETA,


which motor used in electric train ans how much volt.

4 Answers   Trimax,


what is the dedicated neutral earth in ups? y its required?

4 Answers  


what is slip ring induction motor? How it works?

1 Answers  


acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO

0 Answers  






please tell me when we start motor without load in star or delta connection whose current above condition,pl write formula

0 Answers   Foxconn,


All tape of electrical questions Answers tape of motor transformer e.o.t crane

0 Answers   Afcons, Honeywell, Manlift, SIMS,


what is residual current....

1 Answers  


why neutral and body earthing of transformers kept separated? what is distance between two is required as per is?

6 Answers  


what is the change over switch ,switch disconnector ,bypass switch and switch disconnector fuse unit?

1 Answers  


In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?

0 Answers  


for same rating of a transformer and induction motor which one will have higher magnetising current flowing?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)