Why the resistance grounding (NGR) is better than Solid
grounding?
Answers were Sorted based on User's Feedback
Answer / jijo
Ngr is using fault current reduced and flow to ground
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sourabh
Grounding resistors or
reactors are often used in medium voltage systems. These
current limiting devices are connected in series with the
transformer secondary neutral. In the event of a phase-to-
ground fault, the current will flow through, and be limited
by, the neutral resistor or reactor.If a phase-to-ground
fault occurs on any phase cable it will cause fault current
to flow back through
the earth, from the earth into the remote ground, then back
through the grounding resistor to the transformer
neutral.
Is This Answer Correct ? | 1 Yes | 0 No |
NGR: Neutral Grounding Resistance
NGR or grounding transformer using in MV voltage and Soild grounding is using in High & low voltage level as per standards.
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / revathi
In resistance grounding the phases connected to ground
through resistors. it resists the excess flow of current
and trip the circuit.
Is This Answer Correct ? | 2 Yes | 4 No |
Explain how you intend to work under pressure to meet up with deadline target?
What should be the earthing resistance of an industrial substation and also What should be the house hold earthing resistance?
20 Answers Jindal, Pharma, TAAT, TATA,
What’s electric traction?
what is meant by trip circuit supervision & directional or non directional over current ?
what is full wave bridge?
why VCB always installed only at HT yards or HT side? suppose if ACB installed at there means, what will be problem?
at what basis/standard we have to arrive the current density of aluminium/ copper in busbar?
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
3 phase induction motor rotor field rotate at synchronous speed w.r.t ?
whats the reletion betweet flow,pressure,head,rpm and motor rating?
What is the purpose of a process loop? What is the controllers responsibily?
What is basic fundamental for choosing NGR or NGT for any generator neutral grounding